in our sub station why we step down firstly 33kv\11kv then
11kv to 430v. can we direct step down 33v to 430.v.

Answers were Sorted based on User's Feedback



in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / prateek lau

yes it is possible to step down 33kv directly to 430v but
in that the turn ratio of the transformer would be large
and it will increase the size as well as cost of the
transformer.

Is This Answer Correct ?    28 Yes 6 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / devesh mishra

yes we can directly step down from 33/.433kv.
the lv side remains constant for 11 or 33kv & hv side
depends on load i.e,

for load upto 4 mva 11kv ht line is required,whereas
for load above 4 mva 33kv ht line is required.

Is This Answer Correct ?    40 Yes 25 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / cv raman

Genarally load centers are very away from the Generating
stations & scattered too.No of 11/.430KV SS are very high
compared to 33/11KV SS. In the view of construction cost of
the 33/11KV SS is high compared to the 11/.430KV SS. At
this condition , construction cost of 33/0.420KV is very
high compared to the cost of 33/11KV SS. If we propose
33/0.420KV SS in all load centers the no. of ss will become
very high and construction cost will be very high.

Technically we can go for strigh step doun but it is not
economical.

Is This Answer Correct ?    16 Yes 4 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / nilkanth

yes we can do it.

But it is not feasible since
1]feeder were design on constant current (44kV/11Kv-line
from nearest substation to distribution transformer)
2]Distributor lines designs for constant voltage(11kV/440V-
line from distribution transformer to home)

It is normal practise to have less flctuation at load end.

please revert back for any query?


Nilkanth--SIEMENS

Is This Answer Correct ?    16 Yes 7 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / paramesh dutta

Yes, it can be done and it is being done. There are many
such substations with voltage ratio of 33kV/0.433kV.

Is This Answer Correct ?    7 Yes 1 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / gurucharan singh

because of LV circuit breaker current capacity limitation
upto 3 MVA. Can directly step down from any voltage level
to 415V. but 3 MVA only that around 3150 A in Aluminium Bus
bar or 4000A in cu. bus bar. that about 3.5 MVA.

Is This Answer Correct ?    12 Yes 9 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / anuj

Yes we can step-down the voltage directly from 33kV to 430V
but it is not feasible since transformers turns will
increase which will ultimatly increases the cost and
secondly laod centres are far more distance than the S/S
which will increase the LT line and eventually the losses
are more in LT line than the HT line.Therefore from S/S to
the load centres, HT lines are running and near the load
centre distribution transformer is installed.By this way we
can reduce the LT line and ultimatly the losses

Is This Answer Correct ?    5 Yes 2 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / ramesh

Generally we can step up high voltage to low
or low voltage to high voltage for a possible range.
which is balance for our economical stage
but technically it is possible the turn ratio of the
transformer would be large and it will increase the size as
well also differs cost of the transformer.
so that generation for 11 kv increases up-to level ll 750kv
11kv-33kv-66kv--132kv---400kv--750kv
step down as 11kv-440V- 230V-110V

Is This Answer Correct ?    3 Yes 0 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / bk

Technically it is possible to step down voltage level to
430V directly from any upper voltage level. However, our
power system network is connected to local power plant (may
be a CPP) that generates power at 11KV level. therefore it
is requred bring the network power voltage level to 11KV
for distribution purpose.

Is This Answer Correct ?    5 Yes 4 No

in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 3..

Answer / vrs rathore

Yes we can, but if our exixting system is workable for only
11kv and required capacity is more then 4000kva then we
have to take 33kv connection and after that it has to step
down 11kv for supplying our esisting system, which is
working only for 11kv/430v.

Is This Answer Correct ?    3 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

why HT motors are earthed only at equipment side & for it's single core cable with aluminium wire armoure using?

1 Answers   Legrand, NLC Neyveli Lignite Corporation Limited,


explain with the help of loading capability curve,reactive power generation and absorption from synchronous generator?

0 Answers  


explain with diagram how to protect transformers and substations from over current with help of CT's?

0 Answers   BARC,


according to ohms law ,the voltage increases then current is what happened?

4 Answers   NTPC,


can any tell me why slope 40% and 80% is calculated in differential protection?

0 Answers  






Hello Friends, How can we recognize the CT Star Point is S1 or S2 in case of Electro Mechanical Relays and what is meant by Restraining coil in relays and what is the purpose of that.. thank you in advance..

0 Answers   Siemens,


HELLO SIR, IAM PREPARING HPCL EXAMS. SO PLS SEND MATERIAL OF HPCL ELECTRICAL ENG..TO VIJAY_8888@YMAIL.COM

0 Answers   HPCL,


why we use sinosidal voltage / current instead of others in system?

0 Answers  


With a phasor diagram show the effect of increasing the field current of a generator supplying a constant real power and connected to a grid system.

0 Answers   VECL,


when voltage gets down the current of motor increases. but according to Ohm's law voltage is directly proportional to current. plz explain

4 Answers   Maruti Suzuki, TATA,


what do you mean by cl PS CTs? What are technical details required for it's manufacturing?

1 Answers  


what is the diffrence between dol and star delta strater? why star delta starter used instead of dol?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)