why neutral and earth should not be connected on 3 phase
440v/50c/s supply at consumer side. where as on
25kv/ac/50c/s railway traction substation neutral and earth
will be connected and track at substation. and track will
act as neutral and earth. Reasons for this is needed
urgently
Answers were Sorted based on User's Feedback
Answer / nmr
IF ALL CONSUMERS EARTH ARE CONNECTED TO NEUTRAL AT EACH
CONSUMER POINT, ALL THE EARTH ELECTRODES RESISTANCES ARE
BECOMES PARALLEL ALONG WITH TRANSFORMER SECONDARY NEUTRAL-
EARTH ELECTRODES. HENCE 1/R= 1/R1+1/R2+1/R3+1/R4 ETC.,
THERE EFFECTIVE RESISTANCE IS BECOMES VERY VERY LOW. IF A
30 KVA TRANSFORMER IS THERE. THE CURRENT IL/IPHSE =
30,000/440*1.732 = 40.0 AMPS (WITH UNITY PF) THIS CCURRENT
WILL PASS THROUGH EARTHS ELECTRODES(BECAUSE ALL EARTH
RESISTANCES ARE PARALLEL AND NET RESISTANCE WILL BECOME
LESSER THAN THAT OF NEUTRAL)SO STEP POTNTIAL WILL RAISE
CAUSES ELECTRIC SHOCK TO THE PEOPLE WALKING AT NEAR
TFP/PANNEL BOARDS. IN TRACTION SUBSTATION A EARTH MAT WILL
BE PROVIDED IN THE YARD TO REDUCE THE STEP VOLTAGE NOT TO
GET SHOCK BY THE PEOPLE. OK
NMR/email; bapdada1812@gmail.com electrical engineer
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
Consumers earth is for connecting to metal bodies to prevent
shock . The neutral is already earthed at the TC and another
earth means extra expenditure.During earth fault ,there will
be temporary rise in voltage resulting in burning out of
potential coils of the energy meter.And if earth is
connected to neutral wire of supply after the RCCB, it will
trip as a portion of neutral current will be bypassed.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / jicks patel
voltage level at consumer side is generally kept low (230v
or 440v),any shocking moment should face fuse sensually.so
no more cost required like earthing.
| Is This Answer Correct ? | 1 Yes | 2 No |
Difference between mcband isolator
What is error of a measurement?
Electrical breakdown strength of an insulating material depends on............?why because?
what should be the motor rating for pumping water for house hold use from 60km far lake and what formula is to use please tell me
what is Insulation monitoring device. where it is used? (in switchgear room or control panel or in field equipment)
what is different between relay and plc?
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
what is relation between ct and pt ratio with multiplication factor of a energy meter? is there any other factor on which multification factor depend?
What is the difference between magnetic loading and electric loading of a machine?
During underground cabling in landscape area what did we cover the cable with to prevent the electric shock & protect the cable?
how to test generator protection rotor earth fault relay and locked rotor test?
if we supply to secondary winding how transformer work?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)