how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / umesh kumar
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 239 Yes | 45 No |
Answer / khaleel
Lets say
Chiller Capacity 100TR
Power Consumption 70KW
Then IKW/TR = 70/100 = 0.70 KW/TR
| Is This Answer Correct ? | 210 Yes | 22 No |
Answer / r.gandhi
1 KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 120 Yes | 26 No |
Answer / tapan abdul kalam
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 66 Yes | 12 No |
Answer / vivek namdeo
IKW/TR = consume power in k.w./generated chiller TR
| Is This Answer Correct ? | 59 Yes | 8 No |
Answer / palash bolia
1 Ton of Ice = 2000 Pounds(909.1 Kg)
Latent Heat of Ice = 335 kJ/kg
Amount of Heat removed to form 1 ton of (british) ice from
0deg of water to 0deg ice =
(909.1 X 335)/(24 X 3600) = 3.5 KW
| Is This Answer Correct ? | 34 Yes | 3 No |
Answer / sumesh
Here comes the importance of COP which is always greater than 1
Both the answers are correct.
1 Ton = 3.5 kw
but for producing 1tr,only .7-.9 kw/tr(depending on machine).
for more clarification read and understand "coefficient of perfomance"
| Is This Answer Correct ? | 36 Yes | 6 No |
Answer / gaurav majumdar
Basically HVAC Engg know 1 kilocalorie (kcal)= 3.97 Btu
So 1 TR = 3.52 KW
| Is This Answer Correct ? | 32 Yes | 5 No |
Answer / kuna
KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 19 Yes | 4 No |
Hi, We facing one similar problem in our computers i.e we are newly constructed our design department after that shifted our computers but our computer desktop screen is vibrating. we are conducted our electrical maintainance person he told that is UPS problem, then we changed the UPS also again we are facing that problem in that room only. then we put lcd monitors that problem is solved. But in other monitors why the computer desktop screen is vibrating please give a suggestion to me. Regards, Raju.N.G
It is used or not HT cable single core 630 sqmm in LT 3 phase capacitor bank which is used in PCC(power control center).
I have recently seen a transformer which had two primary terminals and was connected between two lines,i would like to know what kind of transformer is it?short discription about it,any advantages,purpose of usage of the same.............
which cable is preferred PVC OR XLPE for voltage from 220V to 11 KV with proper justification
how can we check a fully charged battery?
What is the measuring instrument of magnetic flux density?
what is mean by marshalling box in transformer?
Why strting torqe high in inducation motor?
when any relay trips in any ckt then what type of setting is there in motor?what is function of relay in that ckt?
Is it acceptable of installing an earth pit in planters area where bare copper cable, earth rod and connection are susceptible to corrosion due to water?
If we connect the capacitor banks for DG set for maintainig the power factor, it will effect to alternator windings??????????
how to stop oil leakage in power transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)