why bucholtz relay placed inclined in transformer?
Hi
The bulb of the Buchholz relay contains liquid mercury which
closes the alarm or alarm/trip contacts whenever the relay
is activated. Note that the liquid mercury closes the
alarm contacts only if the gas flow through the relay is
not serious. However, if the flow is serious both alarm and
trip contacts will close to give alarm and trip signals.
From the above explanation you can understand that liquid
mercury being a good conductor must be kept away from the
contacts under normal condition. The only way to do this is
by tilting the relay.
Is This Answer Correct ? | 10 Yes | 4 No |
what is meant by ceiling voltage, ceiling current?? pl reply asap
What is expention fastener (Fan)
why we can choose induction machine in wind mill? why can`t use synchronous machine?
what is the maximum Load capasity in LV-Panel,MDB,SMDB & Final DB'S in Electrical disribution system?
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
Why D.C Voltage used in Meggering...as well as in Hipot test? why not A.C?
What is neutral and how to produced
i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.
0 Answers Bay Fishing Corporation,
what is the difference between analog and digital signal?
how we provide neutral earth on synchronising panel as per electrical standards?
Why delta star trformers are used for lighting loads?
We are having a 2000KVA DG set. It trips with Over speed and Engne Hot when the mahine is stopped in full speed. How shall I analyse the block load and reverse power.Is the problem related to power factor. The machine which runs on this DG is having all Synchronous motors with incividual Drives.