if we know Fault level say 25 KA , How to decide
busbar size for Distribution network of 1000 Amp
Breaker ?
Sample Calculation or Farmula Available or not ?
Answers were Sorted based on User's Feedback
Answer / bala
2nos.*60mm*1omm copper bar is enough for 1000amps breaker.
formula is available
Is This Answer Correct ? | 13 Yes | 9 No |
Answer / ritesh m
When current is high then current density become constant.
You can calculate bus bar size by taking current density 1
J=I/S where j is current density, I current & s cross
section.
Then you can calculate size.
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mehul g. c.
if you know the fault level of that area.
then you should find short circuit current.
if you find that then your busbar should be design for that
much short circuit current.
suppose your fault level is 25 ka & then your short circuit
current is 1500 amp. then your busbar should stand safe at
25 ka for 1 or 2 sec until your breaker tripped.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / subrata
125mm X 10mm aluminium busbar is enough for 1000a current (25kA)
Is This Answer Correct ? | 3 Yes | 2 No |
What are the causes for the failures of sandwich type (Al) busducts?
What is Scott connection? In which device it is used?
(In MEP services) HVAC in AC Plant room what else can we provide if the chiller is not considered?
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
how we can calculate the transformer size.
21 Answers Avalon, Edison, Hyundai,
wwht is wave trap used in ht line
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
For 132 KV line, PT or CVT which is prefered for measuring & protection? is there any IS or IEE standard available?
If there are two transformer having rating of 2.5mva, 6.6kv/440v(satr-star),and the load is 600kw then what is better to maintain less losses in transformer having both transformer in parellel or only single transformer connected to load? Please give calculated answer
What is fault level?How it is calculated and how it is Expressed?
In ac circuit R,L,C are connected in series what is the output the circuit? explain
What is the tension required for the 25000 CFM AHU belt