if we know Fault level say 25 KA , How to decide
busbar size for Distribution network of 1000 Amp
Breaker ?
Sample Calculation or Farmula Available or not ?
Answers were Sorted based on User's Feedback
Answer / bala
2nos.*60mm*1omm copper bar is enough for 1000amps breaker.
formula is available
| Is This Answer Correct ? | 13 Yes | 9 No |
Answer / ritesh m
When current is high then current density become constant.
You can calculate bus bar size by taking current density 1
J=I/S where j is current density, I current & s cross
section.
Then you can calculate size.
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / mehul g. c.
if you know the fault level of that area.
then you should find short circuit current.
if you find that then your busbar should be design for that
much short circuit current.
suppose your fault level is 25 ka & then your short circuit
current is 1500 amp. then your busbar should stand safe at
25 ka for 1 or 2 sec until your breaker tripped.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / subrata
125mm X 10mm aluminium busbar is enough for 1000a current (25kA)
| Is This Answer Correct ? | 3 Yes | 2 No |
Merits & Demarits of Oil circuit & Air circuit breakers ?
WHaT IS THE CONCEPT OF INDUCTION LAMPS IN MODERN LIGHTINGS, and HOW IT WORKS TO EMIT LIGHT ( AS NO ELECTRODES ARE PRESENT ) ?" COULD INDUCTION LAMPS CAUSE INTERFERENCE WITH COMUNICATIONS INTO A STORE USING INDUCTION LIGHTING ? WHAT IS THE BENEFIT OF USING THE LOW FREQENCY INDUCTION LAMP , VERSUS LED , AND VERSUS FLUORESCENT, AND VERSUS ANOTHER KIND OF LIGHTING . THANK yOU MOISES GUINDI
we the the value of frequency is 50 HZ in DG then why we said the value inductive rectance is zero in DG?
how much resistence in proper earthing?
What is the different between conventional MCC and intelligent MCC? Common controller or controller for each bucket
What is the form name of 'c' license, I want to download in web
0 Answers BMM, Ceebros Hotels,
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
why do we prefer a 3-phase delta connected load rather than star connected?
If we have 15000kw connected load in a factory than how much power demand sanction should be taken from electricity board. Pls provide complete calculation.
What is tan delta & PPM in transformer? and whats its IS value?
what are the things that can cause a three phase motor to crawl?
State thevenin’s theorem?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)