how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / shubhabrata sengupta
Chiller IKW/TR
Chiller Rating - 650 TR
Power Consumption – 100 KW
IKW/TR = Consumed Power in KW / Generated chiller TR.
Chiller is running at 34% i.e. 221 Generated chiller TR
Therefore IKW/TR is 100/221 = 0.45
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / balram singh mnadloi
TR= (delta T*flow)/(3.5*0.86)
and
KW=(1.73*V*I*PF)/1000
Then you have to divide TR by KW so you find Ikw of chiller
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shashi
Halo guyz,1TR =3.5KW is not electrical power .it is thermal unit .So don't confuse
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashok
1TR --- 3.5KW
1kw ----8633btu
1TR -----12000BTU
1kw/TR --- 1.396
| Is This Answer Correct ? | 24 Yes | 26 No |
Answer / puneet prashar
As we know that 1 KWh = 3413 btu ( British thermal
unit)But not 1kw, but it is = 8633 btu
and 1 TR = 12000 btu
kw capacity = 12000/8633
Hence 1 TR = 1.39 kW
| Is This Answer Correct ? | 6 Yes | 14 No |
Answer / jitendra patel
IKW in HVAC = (Chilled water TR x 3025)/860
for example Hvac = 200Tr
Ikw = 200*3025/860
=703.48
| Is This Answer Correct ? | 17 Yes | 29 No |
IF I USED VVVF DRIVE IN FAN APPLICATION MOTOR IN 6.6 KV ( 700 KW) MOTOR & DURING NORMAL RUN OPERATION TIME IF RPM SUDDENLY REDUCE IN MOTOR BY DRIVE(E. MOTOR RPM REDUCE SUDENLY 687 TO 550 RPM) WAHT WILL BE HAPPEND IN DRIVE
Why frequency fix in 50 Hz?
what is Wave Trap? And its Function ? Detail? Where it is Used?
What is the diffrence (Technical & Construction ) between CBCT & Normal CT?
For DG set,if the loading is increased,does flue gas temperature increases or not?
what objective books are good for preparing for PSU's?
How can we calculate the Rating of DG Set for a 4 kw motor?
what is the meaning and difference between ELECTRICAL DRAWOUT and MANUAL DRAWOUT?
is it possible to convert electrical energy to light energy for transmission purposes?
seromechanism
in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel ?
IDMT relay are mostly used for protection against..??? 1)Earth Fault 2)Inter turn fault 3)Overloading 4)None of the above
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)