dear friends,
we are use 130 hp load run with 0.98 power factor ( 38KVAR
capacitor connected ). if we need improve the the power
factor to 1 (unity). how much kvar capacitor to be add. have
any formula? please share with me.
Answers were Sorted based on User's Feedback
Answer / jitendra
130*746=96.98kw
kvar=kw(tan pi1-tan pi2)
kvar=96.98(.2030-0)
= 19.68 Kvar
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / bmk mughal
KW=96.98
COS-1.98=11.470
TAN11.470=KVAR1/KW
KVAR1=19.69
COS-11=00
TANO0=KVAR2/KW
KVAR2=0
Required KVAR=KVAR1-KVAR2
=19.69KVAR
| Is This Answer Correct ? | 1 Yes | 0 No |
if u can get P.F= 1 u will get noble prize
| Is This Answer Correct ? | 0 Yes | 1 No |
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
why r use the wave taper in the substation ?
What is the difference between relays and contactor construction wise?
In generating stations which we generate current or voltage if it is voltage then how it will convert to current and power?
can we use heat gun instead of gas torch in 11kv termination kit. I mean can both sources provide enough amount of heat to ensure the uniform shrinkage of sleeve.
we can use airconditioner for cooling the winding of transformer ,if not why?
A T-T transformer can not be parallel with transformer A V-V B star-delta C star-star D delta-delta
what's the meaning of the negative going half cycle in the circuit containing a bulb and a switch in series with a input ac source. i mean what happens in the -ve cycle. the dir. of current changes or any other thing. if dir. changes then why we use fuse in only phase wire.
State the frequency for rc phase shift oscillator?
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
what will be the energy loss =? Voltage drop = ? Conductor resistance at 20 degree C = ? Temprature convertion Factor at 50 degree c = ? on ACSR DOG Condutor at following data. distance = 4.8 kM Load = 2980 kWh Size of Conductor = 6/ 0.186 Volt = 11 kV.
1 Answers Pakistan Atomic Energy Commission PAEC,
What can you contribute to the progress of our Company as an employee if you are selected?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)