dear friends,
we are use 130 hp load run with 0.98 power factor ( 38KVAR
capacitor connected ). if we need improve the the power
factor to 1 (unity). how much kvar capacitor to be add. have
any formula? please share with me.
Answers were Sorted based on User's Feedback
Answer / jitendra
130*746=96.98kw
kvar=kw(tan pi1-tan pi2)
kvar=96.98(.2030-0)
= 19.68 Kvar
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / bmk mughal
KW=96.98
COS-1.98=11.470
TAN11.470=KVAR1/KW
KVAR1=19.69
COS-11=00
TANO0=KVAR2/KW
KVAR2=0
Required KVAR=KVAR1-KVAR2
=19.69KVAR
Is This Answer Correct ? | 1 Yes | 0 No |
if u can get P.F= 1 u will get noble prize
Is This Answer Correct ? | 0 Yes | 1 No |
how to select the double earth conductor if 21A full load?
Name the test signals used in control system
after applying C-License in how many days we get it?
what is the difference between delta-delta, delta-star transformer???
In CT, burden is 15 VA and protection 5P20,CT ratio is 100:1 then what would be the knee point voltage ?
campared to ac, in dc corona loss is
solar inverters was not connected to the nuteral link .this nutwral possible to any other systems
why capacitance effect is predominant in underground cable transmission and inductance effect is predominant in over head line transmission?
WHAT TYPES OF OIL(STRUCTURE) ARE USED IN POWER TRANSFORMER INSULATION?
Define ohm’s law for a.c (alternating current)?
when secondary volts is given how do we find primary volts, turns, amps of primary and secondary given???
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,