how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / nilantha warushavithana
1 TR = 12,000 BTU/h
1 BTU/sec = 1.055 kW
12,000 Btu/h = 3.5166 kW
1 kW = 3412.3 BTU/h
| Is This Answer Correct ? | 14 Yes | 1 No |
Ikw
Power input in kw for per ton of refrigeration KW/TR
FOR EXAMPLE 100TR CHILLER
FOR PRODUCING 100TR POWER CONSUMED 90 KW
IKW /TON = 100 / 90 = 0.9 i.e 0.9 KW /TON
to find IKW,COP,EER
If the power consumption is 1 kw /ton power consumption
system will provide cop of 3.5 and EER will be 12.
| Is This Answer Correct ? | 17 Yes | 7 No |
In general Practice you can consider 1 Tr = 1200 Watt = 1.2
kw
1 TR = 3.5 KW is next to impossible.
| Is This Answer Correct ? | 35 Yes | 26 No |
Answer / sohal
to find out ikw
Amp.X Volts X Power-factor X 1.732/1000= kilowatts
then divided by machine tonnage = input kilowatt(IKW)
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / sandip bharne
1Tr=80x907/24 ( ice requires 80kcal/hr to melt,907 is US
short ton)
=3023 Kcal
1kw= 860kcal/hr
1TR =3024/860
1TR =3.51KW
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / carol
Be Carefull!!!!
TR and W are POWER UNITS
Btu is an ENERGY UNIT
As everyone knows from Basic Physics:
Energy = Power x time
The actual conversions are:
12.000 Btu/h = 1 TR
1 TR = 3517 W
Therefore,
12.000 Btu = 1 TR-h
12.000 Btu = 3517 kWh
Watchout!!!!!.....
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / shri narayan gond
I know that 1 kw = 3413 B.T.U. and 1T.R.=12000 B.T.U. ,1T.R.=12000/3413.=3•5Kw.
Santiry fugle chiller I.K.W.=lode k.w./T.r.
For ex. My chiller capacity is 760 tr. And lode
509 kw.
I.K.W. =509/760
Ikw =0•669
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / pradip
1TR= 12000BTU = 3000KCAL = 3.516KW,It is a thermal Unit,
But IKW relate of Power Consuption of Kw/TR,
In market many HVAC systems area available,so every systems
has different IKW,
Example : for VRV system
1TR consume 0.95 to 1.2KW,
1TR=1.2KW,
so IKW =1.2
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / ruka
1TR=3.5kW <-- Cooling Capacity
3.5kW/COP = Electricity Consumption; normally COP>= 3
COP = Coefficient of Performance
If COP = 3.5
then;
1TR = 1kW <--- Can be varie
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh chavan
we need saving power consumption in HVAC system. please share
| Is This Answer Correct ? | 5 Yes | 1 No |
Give the topology of current amplifier with current shunt feedback?
why put integration for capacitorand differation for inductance
What is the basic principal of Diesel genarator?
3 Answers Juniper Networks, MRF,
What is the meaning of dedicated earthing?
what is the different between rms and average value
is 3-phase induction motor need a starter ? why do it so
hello friends..... any one have papers or any study materials?sail ,hpcl...?
pleasee tell me the risks and hazards of a Cable Jointer job? Thank you.
how much earth resistance consider to commissioning the transformer?
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
how many kw = one ton air condition?
what happens when dc supply is given to the transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)