how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / nilantha warushavithana
1 TR = 12,000 BTU/h
1 BTU/sec = 1.055 kW
12,000 Btu/h = 3.5166 kW
1 kW = 3412.3 BTU/h
Is This Answer Correct ? | 14 Yes | 1 No |
Ikw
Power input in kw for per ton of refrigeration KW/TR
FOR EXAMPLE 100TR CHILLER
FOR PRODUCING 100TR POWER CONSUMED 90 KW
IKW /TON = 100 / 90 = 0.9 i.e 0.9 KW /TON
to find IKW,COP,EER
If the power consumption is 1 kw /ton power consumption
system will provide cop of 3.5 and EER will be 12.
Is This Answer Correct ? | 17 Yes | 7 No |
In general Practice you can consider 1 Tr = 1200 Watt = 1.2
kw
1 TR = 3.5 KW is next to impossible.
Is This Answer Correct ? | 35 Yes | 26 No |
Answer / sohal
to find out ikw
Amp.X Volts X Power-factor X 1.732/1000= kilowatts
then divided by machine tonnage = input kilowatt(IKW)
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / sandip bharne
1Tr=80x907/24 ( ice requires 80kcal/hr to melt,907 is US
short ton)
=3023 Kcal
1kw= 860kcal/hr
1TR =3024/860
1TR =3.51KW
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / carol
Be Carefull!!!!
TR and W are POWER UNITS
Btu is an ENERGY UNIT
As everyone knows from Basic Physics:
Energy = Power x time
The actual conversions are:
12.000 Btu/h = 1 TR
1 TR = 3517 W
Therefore,
12.000 Btu = 1 TR-h
12.000 Btu = 3517 kWh
Watchout!!!!!.....
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / shri narayan gond
I know that 1 kw = 3413 B.T.U. and 1T.R.=12000 B.T.U. ,1T.R.=12000/3413.=3•5Kw.
Santiry fugle chiller I.K.W.=lode k.w./T.r.
For ex. My chiller capacity is 760 tr. And lode
509 kw.
I.K.W. =509/760
Ikw =0•669
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / pradip
1TR= 12000BTU = 3000KCAL = 3.516KW,It is a thermal Unit,
But IKW relate of Power Consuption of Kw/TR,
In market many HVAC systems area available,so every systems
has different IKW,
Example : for VRV system
1TR consume 0.95 to 1.2KW,
1TR=1.2KW,
so IKW =1.2
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / ruka
1TR=3.5kW <-- Cooling Capacity
3.5kW/COP = Electricity Consumption; normally COP>= 3
COP = Coefficient of Performance
If COP = 3.5
then;
1TR = 1kW <--- Can be varie
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh chavan
we need saving power consumption in HVAC system. please share
Is This Answer Correct ? | 5 Yes | 1 No |
gd eve frndz my qstn is how convert sound energy to electrical energy
why sielent pole is used only in hydro generators and not in turbo generators
what is the principle of singkle phase energy meter?
UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?
What is effect of over voltage and under voltage on ACB
what happenes if two voltage source connected in parallel will be connected to load.
What are dcs and plc?
What products have you designed which have entered high volume production?
which protection are used for turbo generator in thermal power plant.
how was the induction stove working?
Mention the disadvantages of low power factor?
Where all & Why resistance grounding is required?