how do you calculate IKW(consumption per TR) in HVAC?
Answer Posted / umesh kumar
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 239 Yes | 45 No |
Post New Answer View All Answers
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
What is meant by positive and negative feedback?
in star-delta tranformer,if the input of star connection is 400/7v 3 kva then what is the output of delta connection?
What is the difference between voltages or potential difference? And what are they?
Can anyone explain me about the RLC based Impulse high voltage generator and how to and operation of Series resonant High voltage reactor...?
What is distance between electrical panel to land ?
we have require a Motor (1500kW, 6.6kV, 50Hz) which shall operate at 1500rpm during 30min and after it shall run on 500rpm during 15min. The same cycle shall be repetitive during the whole working days. Which method is best and economic to achieve such type of task. VFD, VVFD, Pole changing motor etc.
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
Define resonant frequency?
What is force on parallel conductors ?
Why air circuit breaker off due to power failure?
what's producer of XLPE cable laying in undergroung
do anyone out there know where to find a compleete list on acronyms/abbreviations used in offshore electric engineering. MCB - Micro Circuit Breaker, MCCB-Mouldes Case Circuit Breaker, ELCB-Earth Lekage Circuit Breaker, ELMCB- etc.....
What is the difference between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?