Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


three phase 180kva diesel generator can take how much load
in amp and what is formula to get this?

Answers were Sorted based on User's Feedback



three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / mohan

Formula:1.73 X V X I/1000

180X1000/1.73X415 =I

Full load current 250A.

But we should have take only 80%

Is This Answer Correct ?    131 Yes 20 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / santosh jagale.

Generator rating is 180KVA.
Actually all electrical data is made avialable on genrator
name plate by manufacturer.

If you consider the PF is 0.8 Lag.

Then KW=KVA*PF
i.e. KW=180*0.8
=144 KW
P(KW)= 1.732*V*I*PF
Then,

144=1.732*415*I*0.8

I= (144/1.732*415*0.8)*1000
I= 250.42 Amps.

This is the full load current of generator with 0.8 PF &
415V.

In case of DG sets the generator O/P power is restricted by
power of driving engine, beyond that limit you can,t load
the particular generator. You can put upto 125% of to
genrator but not for too long period.

Is This Answer Correct ?    52 Yes 4 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / ranjith18

BETTER AS THUMB RULE
I = kVA X 1.4
ie
180 X 1.4 = 252A (AS FULL LOAD)

Is This Answer Correct ?    45 Yes 6 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / gins

Now a days DG manufactures assuring that the DGs can be
loaded up to 120% of its rated capacity. But it is always
good to design DG for a maximum load of 80% of the rated
capacity to get the maximum efficient running. In your case
You can load a maximum load of 125.8 kW at pf 0.85. So you
have to give an incomer of MCCB with rating suitable for
125.8kW.

W=root3 x VI x pf
so I = W/root3 x V x pf
I think 250A, 16kA, 4Pole MCCB with 80% plug setting may be
suitable for you.

Accordingly select your incomer with suitable kA rating
with respect to your total load.

Is This Answer Correct ?    20 Yes 5 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / mubashar ali

I = KVA/ 1.732*V
or
I = KW/ 1.732*pf*V

u can also use the fector as mantion Ranjith

I = KVA * 1.4

Is This Answer Correct ?    16 Yes 7 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / ahmed umar

Since the Genset Rating is given in KVA as 180KVA.

I think you should calculate the full load Amperage as
follows:

Formula
I=KVAx1000/Root3x400V

ie, 180x1000/1.732(400)
=180,000/692.82
=259A as full load Amperage.

Is This Answer Correct ?    13 Yes 7 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / deepak kapil

VA=1.732xVxI
180x1000=1.732x415xI
I=250A

Is This Answer Correct ?    6 Yes 2 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / ashvini kumar meena

People are unnecessarily trying to guess pf. Its not required.

To calculate KVA quantity you just need voltage and current.

Power factor comes into picture when you are talking about
real power(in KW.)

KVA = &#8730;3 * V * I

Here V is line Viltage and I is Line current. K will be for
Kilo. Here V line is 415=&#8730;3 * 240(phase Voltage) and I to be
fount.

Above Mr. Deepak Kapil in answer have solved it correctly.

Is This Answer Correct ?    2 Yes 0 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / hitesh

(Watt*1000)/(Root3*V*Pf)

Is This Answer Correct ?    2 Yes 1 No

three phase 180kva diesel generator can take how much load in amp and what is formula to get this?..

Answer / adnan khan

180kva x1.44=259.2 ampere/ phase

Is This Answer Correct ?    3 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

What is double throw isolator and single throw Isolator.

1 Answers   KSEB, L&T, Siemens,


what is mean by kneepoint voltage? when it will happen? ( my doubt is, if CT secondary is open means ct get saturation or blas? what are factors are required for calculations? plz give currect anws:

0 Answers  


Can we manually synchronize two DG sets of same ratings manually without using speed biasing ? If yes then how?

4 Answers  


What value of resistance required between Saftey earth and instrunment earth , maximum and minimum values required

1 Answers  


how induction generator works?

3 Answers  


What is the difference between Dielectric and Insulator

9 Answers  


need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.

0 Answers  


How to calculate no of EARTH PIT? Describe the formula as per IS standard?

0 Answers  


What is the output of below program? #include <stdio.h> int main() { int p,q; for(p=1,q=1;p<7;p++) { printf("%d%d__",p,q); } return 0; } Answers- 1. 17__27__37__47__57__67__ 2. 11__21__31__41__51__61__ 3. __11__21__31__41__51__61__ 4. Compilation error

1 Answers  


how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation

1 Answers  


why various test are performed on electrical panels & power cables before commissioning on site & what are these test???

0 Answers   Lavasa,


How Negative Phase Sequence Relay works in case of Synchronous Motor?

4 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)