Answer / mohan
Formula:1.73 X V X I/1000
180X1000/1.73X415 =I
Full load current 250A.
But we should have take only 80%
| Is This Answer Correct ? | 131 Yes | 20 No |
Answer / santosh jagale.
Generator rating is 180KVA.
Actually all electrical data is made avialable on genrator
name plate by manufacturer.
If you consider the PF is 0.8 Lag.
Then KW=KVA*PF
i.e. KW=180*0.8
=144 KW
P(KW)= 1.732*V*I*PF
Then,
144=1.732*415*I*0.8
I= (144/1.732*415*0.8)*1000
I= 250.42 Amps.
This is the full load current of generator with 0.8 PF &
415V.
In case of DG sets the generator O/P power is restricted by
power of driving engine, beyond that limit you can,t load
the particular generator. You can put upto 125% of to
genrator but not for too long period.
| Is This Answer Correct ? | 52 Yes | 4 No |
Answer / ranjith18
BETTER AS THUMB RULE
I = kVA X 1.4
ie
180 X 1.4 = 252A (AS FULL LOAD)
| Is This Answer Correct ? | 45 Yes | 6 No |
Answer / gins
Now a days DG manufactures assuring that the DGs can be
loaded up to 120% of its rated capacity. But it is always
good to design DG for a maximum load of 80% of the rated
capacity to get the maximum efficient running. In your case
You can load a maximum load of 125.8 kW at pf 0.85. So you
have to give an incomer of MCCB with rating suitable for
125.8kW.
W=root3 x VI x pf
so I = W/root3 x V x pf
I think 250A, 16kA, 4Pole MCCB with 80% plug setting may be
suitable for you.
Accordingly select your incomer with suitable kA rating
with respect to your total load.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / mubashar ali
I = KVA/ 1.732*V
or
I = KW/ 1.732*pf*V
u can also use the fector as mantion Ranjith
I = KVA * 1.4
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / ahmed umar
Since the Genset Rating is given in KVA as 180KVA.
I think you should calculate the full load Amperage as
follows:
Formula
I=KVAx1000/Root3x400V
ie, 180x1000/1.732(400)
=180,000/692.82
=259A as full load Amperage.
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / ashvini kumar meena
People are unnecessarily trying to guess pf. Its not required.
To calculate KVA quantity you just need voltage and current.
Power factor comes into picture when you are talking about
real power(in KW.)
KVA = √3 * V * I
Here V is line Viltage and I is Line current. K will be for
Kilo. Here V line is 415=√3 * 240(phase Voltage) and I to be
fount.
Above Mr. Deepak Kapil in answer have solved it correctly.
| Is This Answer Correct ? | 2 Yes | 0 No |
What are series and parallel isolators?
A 3ph load of 10 KW is equal to how many KW of single phase .
what is main parts of alternator.
the process cynide is used for?
Current Transformer's star point must face the protected object for the relay operation?
we have 3.5MVA-11/6KV transformer. how can we calculate earth fault current and NGR calculation?
how MW increase when steam input increase in turbine.
if a motor is running at 1500rpm then how you can find its HP
What is the difference between diesel generator engine with and without turbo charger with the same capacity?
when we connect a CT in the line will there be any loses in the line due to the mutual inductance of the CT.
ELECtrical
2 Answers Bahwan Engineering, Bhel, Electrosteel, NBCC, Qatar Airlines,
how tan-delta test is performed?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)