three phase 180kva diesel generator can take how much load
in amp and what is formula to get this?
Answers were Sorted based on User's Feedback
Answer / mohan
Formula:1.73 X V X I/1000
180X1000/1.73X415 =I
Full load current 250A.
But we should have take only 80%
| Is This Answer Correct ? | 131 Yes | 20 No |
Answer / santosh jagale.
Generator rating is 180KVA.
Actually all electrical data is made avialable on genrator
name plate by manufacturer.
If you consider the PF is 0.8 Lag.
Then KW=KVA*PF
i.e. KW=180*0.8
=144 KW
P(KW)= 1.732*V*I*PF
Then,
144=1.732*415*I*0.8
I= (144/1.732*415*0.8)*1000
I= 250.42 Amps.
This is the full load current of generator with 0.8 PF &
415V.
In case of DG sets the generator O/P power is restricted by
power of driving engine, beyond that limit you can,t load
the particular generator. You can put upto 125% of to
genrator but not for too long period.
| Is This Answer Correct ? | 52 Yes | 4 No |
Answer / ranjith18
BETTER AS THUMB RULE
I = kVA X 1.4
ie
180 X 1.4 = 252A (AS FULL LOAD)
| Is This Answer Correct ? | 45 Yes | 6 No |
Answer / gins
Now a days DG manufactures assuring that the DGs can be
loaded up to 120% of its rated capacity. But it is always
good to design DG for a maximum load of 80% of the rated
capacity to get the maximum efficient running. In your case
You can load a maximum load of 125.8 kW at pf 0.85. So you
have to give an incomer of MCCB with rating suitable for
125.8kW.
W=root3 x VI x pf
so I = W/root3 x V x pf
I think 250A, 16kA, 4Pole MCCB with 80% plug setting may be
suitable for you.
Accordingly select your incomer with suitable kA rating
with respect to your total load.
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / mubashar ali
I = KVA/ 1.732*V
or
I = KW/ 1.732*pf*V
u can also use the fector as mantion Ranjith
I = KVA * 1.4
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / ahmed umar
Since the Genset Rating is given in KVA as 180KVA.
I think you should calculate the full load Amperage as
follows:
Formula
I=KVAx1000/Root3x400V
ie, 180x1000/1.732(400)
=180,000/692.82
=259A as full load Amperage.
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / ashvini kumar meena
People are unnecessarily trying to guess pf. Its not required.
To calculate KVA quantity you just need voltage and current.
Power factor comes into picture when you are talking about
real power(in KW.)
KVA = √3 * V * I
Here V is line Viltage and I is Line current. K will be for
Kilo. Here V line is 415=√3 * 240(phase Voltage) and I to be
fount.
Above Mr. Deepak Kapil in answer have solved it correctly.
| Is This Answer Correct ? | 2 Yes | 0 No |
What are the types of earthing? Explain dagramatically.
how we can save the power ? suppose the electricity board gives 11 kw , but the machine require only 8 kw means how we can save the exese energy
WHAT TYPES OF OIL(STRUCTURE) ARE USED IN POWER TRANSFORMER INSULATION?
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
depletion layer will form beforre biase or after bias ?
What is the calculating formula for HT and LT amps in a transformer.
On which side, taps are provided in tap changing transformers and why?
EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.
figure of phasor diagram of transformer when full load or no load ?
how to calulate transformer secodary fault A?
What is the difference between a Vacuum Circuit Breaker and a Load Break Switch?
How to find earthfault location in long cable layed underground or outside.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)