three phase 180kva diesel generator can take how much load
in amp and what is formula to get this?
Answers were Sorted based on User's Feedback
Answer / mohan
Formula:1.73 X V X I/1000
180X1000/1.73X415 =I
Full load current 250A.
But we should have take only 80%
Is This Answer Correct ? | 131 Yes | 20 No |
Answer / santosh jagale.
Generator rating is 180KVA.
Actually all electrical data is made avialable on genrator
name plate by manufacturer.
If you consider the PF is 0.8 Lag.
Then KW=KVA*PF
i.e. KW=180*0.8
=144 KW
P(KW)= 1.732*V*I*PF
Then,
144=1.732*415*I*0.8
I= (144/1.732*415*0.8)*1000
I= 250.42 Amps.
This is the full load current of generator with 0.8 PF &
415V.
In case of DG sets the generator O/P power is restricted by
power of driving engine, beyond that limit you can,t load
the particular generator. You can put upto 125% of to
genrator but not for too long period.
Is This Answer Correct ? | 52 Yes | 4 No |
Answer / ranjith18
BETTER AS THUMB RULE
I = kVA X 1.4
ie
180 X 1.4 = 252A (AS FULL LOAD)
Is This Answer Correct ? | 45 Yes | 6 No |
Answer / gins
Now a days DG manufactures assuring that the DGs can be
loaded up to 120% of its rated capacity. But it is always
good to design DG for a maximum load of 80% of the rated
capacity to get the maximum efficient running. In your case
You can load a maximum load of 125.8 kW at pf 0.85. So you
have to give an incomer of MCCB with rating suitable for
125.8kW.
W=root3 x VI x pf
so I = W/root3 x V x pf
I think 250A, 16kA, 4Pole MCCB with 80% plug setting may be
suitable for you.
Accordingly select your incomer with suitable kA rating
with respect to your total load.
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / mubashar ali
I = KVA/ 1.732*V
or
I = KW/ 1.732*pf*V
u can also use the fector as mantion Ranjith
I = KVA * 1.4
Is This Answer Correct ? | 16 Yes | 7 No |
Answer / ahmed umar
Since the Genset Rating is given in KVA as 180KVA.
I think you should calculate the full load Amperage as
follows:
Formula
I=KVAx1000/Root3x400V
ie, 180x1000/1.732(400)
=180,000/692.82
=259A as full load Amperage.
Is This Answer Correct ? | 13 Yes | 7 No |
Answer / ashvini kumar meena
People are unnecessarily trying to guess pf. Its not required.
To calculate KVA quantity you just need voltage and current.
Power factor comes into picture when you are talking about
real power(in KW.)
KVA = √3 * V * I
Here V is line Viltage and I is Line current. K will be for
Kilo. Here V line is 415=√3 * 240(phase Voltage) and I to be
fount.
Above Mr. Deepak Kapil in answer have solved it correctly.
Is This Answer Correct ? | 2 Yes | 0 No |
what is the use of power transformer in GSS.
0 Answers College School Exams Tests, DLF, TCS,
How check electrical motor winding.
what is tan delta point in a current transformer?
what is the thumb rule to know current carrying capacity of copper conductors of different size.
why transformer is rated in kva?
why we use to transmit the power in three phases intead of single phase ?
how to synchronize 3 phase slip ring induction motors of different ratings.
For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details.
I have a generator of 300kw.400V,50hz . what is means can i assume the load Red Phase with Neutral 300kw.Yellow phase with neutral 300kw and Blue with neutral also 300Kw. or - red with neutral 100kw same as yelloe and blue phase also giving 100kw with neutral respectively
how much watts are equal to one unit of energy meter?
i need the curve duty cycle and amper for (150 kva @50% dyty cycle) transformer turn ratio :19 and vin 400
i am electrical engineer i cant get job in pure electrical industry ,but i got job in instrumentation field whether there is good scope for me, as i am fresher i m not well with the industrial trends so any experienced engineer pls reply me