three phase 180kva diesel generator can take how much load
in amp and what is formula to get this?
Answers were Sorted based on User's Feedback
Answer / sachin kusumkar
For continuous loading of a dg set,
Amps= KVA*1.4*Efficiency
= 180*1.4*0.8
=201.6
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sachin trinagariwar
i think there is no need to go to such formule one thing
and we need to run the generator on 80% load only
so we can consider the rating as follows
180 kva means 180 A
250 kva means 250 A ans so on
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / elangkumanan
kva =kva*1000
-----------
1.732*v*i*cos0
180*1000
= --------
1.732*440*i*0.85
I =180000
--------=278 A
647.768
| Is This Answer Correct ? | 4 Yes | 5 No |
On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?
what is meant by magnetic flow meter ? explain its working principle ?
you have an automatic voltage regulator at home for your appliances,if the voltage in your area drops from 220v to 190v,does the output of the automatic voltage regulator drops?or does it retains the 220v output?
Difference between control junction box (cjb) and power junction box(pjb)?
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
how can we chack a capacitor in acircuit
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
What do you mean by phasors?
in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?
What kind of preventive maintenance are there for AC induction motor?
would you please give me any idea about the BARC interview question on electrical? i have an interview on 1st july.....plz hlp me.......its urgent......
why breaker closing coil gets burnt if supply is continously provided to it.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)