For testing 33kv cable hipot testing. How much kv we have to
Apply .Give in details.
Answers were Sorted based on User's Feedback
Answer / zahid ali
2E + 1 KV = 67 KV DC Hi pot
67 * .707 = 47 KV AC Hi pot
Is This Answer Correct ? | 119 Yes | 57 No |
Answer / bapi
AS HI POT TEST IS CONDUCTED IN DC SO APPROX. 1.5 TIMES OF
AC SUPPLY VOLTAGE IS APPLIED FOR 1 MINUTE.
FOR 33 kV CABLE APPROX. 50kV FOR 1 MINUTE WILL BE APPLIED.
FOR TESTING OF "R" PHASE WE HAVE TO SHORT "Y" AND "B" PHASE
ALONG WITH ARMOUR & IT SHOULD BE EARTHED. SIMILARLY FOR Y &
B PHASE.
AFTER EACH PHASE TESTING IT SHOULD BE DISCHARGED THROUGH
DISCHARGE RODS.
Is This Answer Correct ? | 66 Yes | 30 No |
Answer / s.jeganath
(2E+1)1.414=dc
2E+1 =AC
(2*33000+1)1.414=DC
67000*1.414=DC
94738v=DC (it is a 100%)
but apply in 80% only it is standard for 33kv cable
APPly voltage dc=94738*0.8=75790V
(75.790KV DC)
Is This Answer Correct ? | 43 Yes | 18 No |
Answer / mathiraja
2E+1KV=67KV FOR AC VOLTS
(2E+1KV)*1.414=94.73KV FOR DC VOLTS
ACCORDING TO IEC60950 STANDARDS.
Is This Answer Correct ? | 22 Yes | 2 No |
Answer / manikandan n
For DC Hipot test the applied voltage calculating formula is equal to (2E+1000)*1.414*(80/100)
E = system voltage
1.414 = For DC RMS conversion.
80% = test conduct in site at second time.
Is This Answer Correct ? | 19 Yes | 4 No |
Answer / ram sundar
For DC HIPOT = 1.414*(2E+1)
E=33/1.73=19.07
DC Hipot = 1.414*(2*19.07+1)
55.34kv approx 56Kv
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / sunil choudhary
FOR TESTING 6.6KV CABLE HIPOT TESTING.HOW MUCH KV WE HAVE
TO
APPLY .GIVE IN DETAILS.
sunil choudhary
Is This Answer Correct ? | 20 Yes | 15 No |
Answer / yousaf
D.C. voltage equal to 3 x U0 shall be applied for 15 minutes. The standard is 1EC5840.
57KV FOR 15 MIN.
Is This Answer Correct ? | 9 Yes | 5 No |
Answer / jim sreedharan
For 33 KV cables we do three tests.
1. Vlf Test: We apply 10 kv dc between graphite and armour
at a low frequency (normally between 0.02 hz to 0.05 hz)
for 1 hour.
2. Insulation Resistance :- We apply 5 kv dc for 1 min
3. High Voltage ac Test:- We apply 57.1 kv for 30 mins
(33/1.732)x 3 = 57.1 kv
God Bless
Is This Answer Correct ? | 12 Yes | 9 No |
Answer / jayasanker
33KV CABLE
FORMULA:2E+1*1.414
2*33+1*1.414 = 94KV DC
IF BUS BAR 2*33+1 = 67KV AC
Is This Answer Correct ? | 8 Yes | 5 No |
What about Reactive power.and role of that one?
If 440 V supply has given at the secondary winding of transformer at that time if we apply 11 KV at primery then what will happen???????
how to calculate the power loss of cable?
How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.
DIFFERENCE BETWEEN TRANSFORMER AND CURRENT TRANSFORMER?
What is maximum demand?How can we caluclate it?
Why Transformer does not work in DC ?
Why fuse is? What will prevent by fuse?
how is differential relay working in transformer.comparison with generator defferntial relay
How does a television work?
Which of the following plant has less plant factor ? -Nuclear -Hydro -Diesel -Pumped storage
if we convert ampers into kw,which one formula use by us,pls tell me?