what is tan delta point in a current transformer?
Answers were Sorted based on User's Feedback
Answer / bhavesh chauhan
First of all let us know what is Tan Delta......?
Tan Delta Testing of a transformer or a CT or a PT determines integrity of insulation of the equipment which determines the remaining life of the equipment. Tan Delta is also called as loss angle or Dissipation Factor Testing.
In a perfect capacitor the curve of voltage vs current are phase shifted by 90..in case if any impurities are present the phase shift wont be 90 degree any more which means it will be less than 90. Thus by measuring new angle developed less than 90 we can calculate the loss angle or the level of insulation.
Measuring of Tan Delta is very simple..We have a Tan Delta Kit which has two terminals coming out of it. Applying the two terminals on top and bottom of the equipment and injecting the current through kit we can get the values of the test..
Tan delta Point is nothing but a point covered by a nut bolt on the bottom side of Bushing of transformer and CT..............
Is This Answer Correct ? | 34 Yes | 14 No |
Tan Delta point in the CT is located at the bottom of the CT. It is provided specifically for TanD testing so that we can find the capacitance and TanD between CT primary and its structure.
It is It is usually connected to ground. But at the time of test, it should be separated from ground and should be connected to LV lead from the TanDelta test set.
Is This Answer Correct ? | 3 Yes | 0 No |
why the transformer primary and secondary windins vector groups vary? why it is something like Dy11 and not as Dy or Yy...
A LT ckt i mean 440 volt flow of current100A.at this time HT current what will ON 11 KV &33 KV.plz givemy answer with example
What is required of exietation to the alternater.
where solid grounding and where grounding through ngr done and why?
Differcence between UPS and Inverter.
What is the difference between surge arrestor and surge capacitor?
2 Answers Shreem Electric Ltd,
What are the different sign conventions used in electric circuits?
Why current Transformer is rated by 100A/5A/5A?
I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.
what is the difference between power transformer & distribution transformer and what are their ratings respectively?
WHAT IS THE DG OIL SPECIFICATIONS AND WHAT IS THE DIFFERENCE BETWEEN THE DG OIL AND TRANSFORMER OIL
how much cable size required for 70 kilowatt load.