Answer / bhavesh chauhan
First of all let us know what is Tan Delta......?
Tan Delta Testing of a transformer or a CT or a PT determines integrity of insulation of the equipment which determines the remaining life of the equipment. Tan Delta is also called as loss angle or Dissipation Factor Testing.
In a perfect capacitor the curve of voltage vs current are phase shifted by 90..in case if any impurities are present the phase shift wont be 90 degree any more which means it will be less than 90. Thus by measuring new angle developed less than 90 we can calculate the loss angle or the level of insulation.
Measuring of Tan Delta is very simple..We have a Tan Delta Kit which has two terminals coming out of it. Applying the two terminals on top and bottom of the equipment and injecting the current through kit we can get the values of the test..
Tan delta Point is nothing but a point covered by a nut bolt on the bottom side of Bushing of transformer and CT..............
Is This Answer Correct ? | 34 Yes | 14 No |
Tan Delta point in the CT is located at the bottom of the CT. It is provided specifically for TanD testing so that we can find the capacitance and TanD between CT primary and its structure.
It is It is usually connected to ground. But at the time of test, it should be separated from ground and should be connected to LV lead from the TanDelta test set.
Is This Answer Correct ? | 3 Yes | 0 No |
what happens when you connect a.c and d.c supplies
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
How to check op amp using multimeter
Why Trasformers rated in KVA
13 Answers College School Exams Tests, HAL, Oil and Gas Jobs,
What is the basic difference between earthing, ground and neutral?
What is the meaning of ST and HT in electrical transmission and what are thier range.
Why DC current is not used in transformer?
1.What is the difference between isolators and circuitbreakers? 2.What is bus-bar?
oil sample dielectric test gives the insulation rupture voltage at 26 kv. is this transformer safe to be operated . The working voltage is 11 kv
sir pls tell me . our ct specifications are 120/5 ,2 core , 0.2 and 5p10 class , 30va and 30va buden. insted of 30 va i want use 15 va. can i use?
what is the significance of 3.5 core cable? or what does this half core mean and why is it required?
WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SIZES??
14 Answers Dubai Group, Saudi Delta Groups, Savitha Electricals,