Answer / bhavesh chauhan
First of all let us know what is Tan Delta......?
Tan Delta Testing of a transformer or a CT or a PT determines integrity of insulation of the equipment which determines the remaining life of the equipment. Tan Delta is also called as loss angle or Dissipation Factor Testing.
In a perfect capacitor the curve of voltage vs current are phase shifted by 90..in case if any impurities are present the phase shift wont be 90 degree any more which means it will be less than 90. Thus by measuring new angle developed less than 90 we can calculate the loss angle or the level of insulation.
Measuring of Tan Delta is very simple..We have a Tan Delta Kit which has two terminals coming out of it. Applying the two terminals on top and bottom of the equipment and injecting the current through kit we can get the values of the test..
Tan delta Point is nothing but a point covered by a nut bolt on the bottom side of Bushing of transformer and CT..............
| Is This Answer Correct ? | 34 Yes | 14 No |
Tan Delta point in the CT is located at the bottom of the CT. It is provided specifically for TanD testing so that we can find the capacitance and TanD between CT primary and its structure.
It is It is usually connected to ground. But at the time of test, it should be separated from ground and should be connected to LV lead from the TanDelta test set.
| Is This Answer Correct ? | 3 Yes | 0 No |
how to calculate the kw, Amps consumed by a capacitor, give me the formula for KVAr into capacitance,KVAr into KW & KVA, Amps
will the power consumption remains the same when speed of the fan cnanges??if so y??
why does not tester light up when it is touched to neutral of 3 pin socket.
How can step up and step down process in power transformer
1 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
why names such like dog ,rabbit, osprey,ant are used for conductors.
Why alternators are designed at 0.8 pf lag?
I want to know which cable would be best to carry 125A current to a distance of 50m. Voltage is 3phase. Kindly share the formula with answer.
1 Answers Medway Educational Consultant,
which technique servo motor tested o.k or faulty ?
why free wheeling diode is connected across inductive load
16 Answers NTPC, Omaxe, Wipro,
why skin effect is decreases with decrease with frequency? why skin effect occur
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
distribution transformer de-rating formula on over limit iron losses
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)