Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I want formula to calculate cable size as per load given in
kw & amp.I searched many sites but didn't right answer.Plz
reply me asap.

Answers were Sorted based on User's Feedback



I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / er. ankush miglani 0971815107

sorry i dont have the xat formula for that but
for ALUMINIUM CABLE: 1sq.mm = 1.2 A of current
CU: 1sq.mm = 5.0 A of current
and the relation b/w A & KW IS
1KW= 1000*A*240*COS#
A- CURRENT
240= VOLTAGE
COS# = POWER FACTOR (.8 TO .99)
NOW IF U KNOW THE EXACT CURRENT LOAD OR LOAD IN THE FORM OF
KW U CAN EASILY FIND THE AMPERE RATING.
AFTER FINDING THE AMPERE RATING U CAN CALCULATE THE THE
SIZE OF THE CABLE. ANKUSH MIGLANI
9718151073
ankushmiglani2000@gmail.com

Is This Answer Correct ?    536 Yes 298 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / tharik

good

3phase cable size calculation formula

Is This Answer Correct ?    346 Yes 121 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / bala

Hai
First u will convert the KW OR kvA loads to AMph
After u can select the suitable cable from cable manufuture
catalouge . that u will consider derating factor = 0.72
For Example
50 A
16 SQ XLPE Al cable may be suitable
The 16 sqmm cable suitable for 70A ( DATA TAKEN FROM
HAVEELS CATALOUGE)
70 * 0.72 = 50.4 A
So the cable suitable for the above load.
after u will cross check voltage drop for the cable

Is This Answer Correct ?    121 Yes 48 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / robert nithin

mv= (VD*1000)/L*I

VD= VOLTAGE DROP(AS PER COUNTRY STANDARDS)
L = LENGTH OF CABLE
I = CURRENT RATING
I = P/(1.73*V*PF)
PF= POWER FACTOR
MV= MILLI VOLTAGE DROP/AMP/METER

SELECT THE CABLE DEPENDING UPON THE MV RATING IN PRODUCT CATALOGS

Is This Answer Correct ?    121 Yes 60 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / anupam mathur

Cable size depends on 1)Voltage Drop, 2)Distance, and 3)Load
So u have to calculate first the permissible voltage drop.
For lighting circuit permissible voltage drop:
2% of the rated voltage + 1 volt
2 X 230 /100 +1 = 460/100 + 1 volt = 5.6V

For motoring load
5% of the rated voltage

5 X 415/100 = 20.75 V

Now the formula for calculating voltage drop:

Voltage Drop = I X D (r X 0.85 + Xc X 0.53)/No. of runs X 1000
I : Current
D : Distance
r : Resistance
Xc : Capacitive reactance

If the voltage drop comes within the limits then ur cable
selection is ok.

Is This Answer Correct ?    94 Yes 50 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / bala

Hai
The formula is delda v =
rt3 x I X Z X L/ 1000 x no OF runs
% OF VOLTAGE DROPS = Deta v
------ X 100
APPLIED VOLTAGE
The % of voltage voltage drops should be below 3 %
I = Requird current
Z = Cable impedance
L = cABLE LENGTH

First how many Amp you required
Example - 80
then you go to cable catalouge find out suitable cable
size
then calculate original current carring capacity of that
cable and multifly with 0.72 ( derating factor )
example in catalouge may be 35 sq mm cable and current
carring capacity may be 125 A
125 X 0.72 = 90
The carring carring capacity point of view this cable will
be ok
next you will check voltage drop with help of above said
fomula

Is This Answer Correct ?    63 Yes 31 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / tauqeer hussain

We can use fromula for Voltage Drop Calculation
VD = mVxIxL/1000
VD = Voltage Drop
mV = Milli Volt(Given Rating Cable Manufacture)
Example 16sqmm mV =2.5 mv/a/m
I = Load Current
L = Lenght of Cable
Exapmle #
Voltage = 415vAC, Ampere = 25, Length of Cable = 100Meter

VD = 2.5x25x100/1000
= 6250/1000
= 6.25 (in volt)
= 1.50% (in percent)

Is This Answer Correct ?    35 Yes 8 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / mohammed motawe

i will give you the basic eqaution,

PL = V*I*Pf=S*Pf ; i need to calculate the load current ,

I= PL/(V*Pf); as per ADDC(abu dhabi electricity), Pf=0.9
V=230 volt,

From the load CURRENT i can choose the rated current of
cable, take into account the voltage drop, so refer to
cataloge of any cables and wires company like oman cables

regarding with three phase just put cu(3) in the equations
best regards

Is This Answer Correct ?    106 Yes 87 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / premgin

See dear the basic soultion to cable size calculatiion in
sismple form can be done like this

Vd= ( mv* I * lenghth)*100/(400*1000)

I u can calualte from the Kw value for the particular pf
simple P/554

L required length

mV is the volatage drop/amp/km that can be obtained for the
particluar size of cable from supplier

eg. for 4cx16 its around 2.5 for most suppliers

100/400 is just amultiplication factor for converting it in
to 3 phase


Now do calulation and check if voltage drop limit is below
2.5 or 4 as per your standards


Simple.

But be cutious this is the simplest method and suitabel
method,many factors like grouping factor,derating
factor,spacing factor,type of laying,etc has to be taken
for apt analysis

Software like E Tap can also be utilised

Is This Answer Correct ?    59 Yes 43 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / tushar jana

I dont understand why people are complicating the issue....
the answer is very simple.

Consider Cable selection for the 3ph motor of 1kW

Formula>> P= root(3) x V x I x Cos(Phi) x Eff
p= power... Say 1kW
V= voltage (415Volt)
I= Unknown
Cos(phi)= 0.85.. say
Eff= Efficiency..= 0.85... say

Now,calculating this, we get>> I= 1.9Amp.. say approx 2A

Now derate this current (bcoz, cable will be laid in duct
or undergroung,etc) consider derating factor as 0.7 (say)
Then current is 2A/0.7=2.85A... say 3A..

now see the cable catlogue of any company.. say polycab..
See which size of cable can carry 3A current and use it...
thats it..

Approx.. for 1kW motor, 3Cx 2.5 Sq.mm cable is sufficient
upto 275m length.

NOTE: This is rough method of calculation. If cable length
is more or motor size is more... then voltage drop
calculation is also to be done.

Contact- 9665065050

Is This Answer Correct ?    19 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,

0 Answers   Jomel,


what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than telling the penality n all

5 Answers   NCC,


How a capacitor discharge weld power supply works? what is the use of a pulse transformer?

0 Answers  


bitumar

0 Answers   Bhel,


Why we have use 3 & 1/2 core cable use for general electrical supply arrangement

1 Answers  


In Railway,why we are used HT Line 25KV ?.why we are not used 11KV,33KV and others for This?

37 Answers   Airtel, BSNL, RRB,


Two bulbs of 500w and 200w rated at 250 v will have resistance ratio as ?

2 Answers   CGL, Dreamz Infra, Sunny Developers,


my 10 hp submersible pump is tripping when connected through ELCB.I have checked the megger value of the coil's with body.It was found to be 0.2mega ohm.that is leakage is there.But when connected to mccb it is not tripping.no leakage current in the motor.Is it safe to connect to mccb? what are the problem's will arise if future?also tell me in ELCB no neutral is connected to motor.than how ELCB was working?

1 Answers  


what is difference between power transformer and distribution transformers

1 Answers  


Is it possible Z axis excess error alarm reflect in X axis if yes explain ?

0 Answers  


why we are using KVA rating for transformer,not KWh rating?

5 Answers   NTS,


what is an S.C.R. and how do they work?

4 Answers   GE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)