I want formula to calculate cable size as per load given in
kw & amp.I searched many sites but didn't right answer.Plz
reply me asap.
Answers were Sorted based on User's Feedback
Answer / amit kumar tripathi
PERCENTAGE OF VOLTAGE DROP IS EQUAL TO
% V DROP = 1.732*Ir*L/1000 ( R COSØ + X SIN Ø ) / V * N
WHERE
Ir = FULL LOAD CURRENT
L = LENGTH OF THE CABLE
R = RESISTENCE OF THE CABLE
X = REACTENCE OF THE CABLE
COSØ = 0.8
SINØ = 0.53
V = VOLTAGE
N = NO. OF RUN CABLE
MAXIMUM % VOLTAGE DROP CONSIDERED 6% As per IE Rule & it cable size designs is Economical.
If Power rating & required cable length is increase , so your cable size is also increase.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / muhammad usama qadir
you can calculate cable size by this link
http://www.solar-wind.co.uk/cable-sizing-DC-cables.html
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / tariqusman
if u want to find the cable size for a specific load. so u
find the load current. and just divid by 4, similsrly u
find the accurate size of cable for specific load. for
example. a load of 50kw, ist u find the load current, and
then divide by 4.
P = 50kw or 50,000watt
V = 440 volt
I = ?
p = 1.7320*440*I*0.8
I = p/1.7320*440*.8
I = 50,000/598.4
I = 83 Ampere
now u divid the load current by 4
83/4 = 20 sq.mm
its simple if u find the cbale size...
| Is This Answer Correct ? | 10 Yes | 8 No |
hai am also no exact answer
may be
eg 5HP motor select cable size 2.5sqmm cu cable, r 4 sqmm
Al cable.
work out
5Hp motor taken 90% full load current 7 amps.
that current * 5 times = 35 Amps (motor not run in full load
its my experiance)
2.5sqmm cu cable full load withstand current 36A
4sqmm Al cable full load with stand current 34A
so we choice Cu r Al cable
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / sukhvinder singh
Kv*load/volt
for single phase use 230 volt& for three phase use 440 volt
Kv =1000
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / amit kumar tripathi
The Power Cable size shall be selected on the basis of
(a) Full load of Current Carrying Capacity
(b) Fault current Rating
(c) Steady state voltage drop
(a) Full load of Current Carrying Capacity
Transformer TRF-1 Rating (P) = 1600 KVA
Rated System Voltage (V) = 0.4 KV
Minimum size is required for full load current =P/_/3 x V
=2309.47Amps
Overall derating factor of multicore LV cables =0.660
From Cable catalogue, 1C x 400 Sqmm cable is selected and
Current rating of the cable in air = 680Amps
Therefore 6 cables Run is selected= 4080 Amps
Hence selected cable size is adequate
(b) Fault Current Rating criterion
Since feeder is protected by circuit breakekr, cable size is decided based on the bus of Fault current the transformer feeder .
The required size of cable for fault current is given by
formula =Isc. _/t
K
where,
Isc - Short circuit current in KA = 50KA
t - Fault Clearing time in seconds =1Sec
K - XLPE insulation factor = 0.094
Therefore required cable size = 531.91Sq mm
Hence, Actual cable size choose 6 Run - 1C x 400 Sq mm is adequate
(C) Steady state voltage drop
Ir - Full load current of motor = 2309.47Amp
Rated System Voltage (V)= 400V
Cos Ø = 0.85
Sin Ø = 0.53
L - length of the cable =5
N - No of cable runs per feeder =6 Run
R - Resistance of 1C x 400 Sq mm cable =0.104 Ohm / km
X - Reactance of 1C x 400 Sq mm cable =0.07 ohm / km
The voltage drop is given by formula =
√3 x Ir x L/1000 (R cosø1 + X sinø1)/N X V
Therefore voltage drop =0.1044 %
Voltage drop is less than permissible value of 6%
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / er. naushad ashraf
Dear See 1 eg. of Cable Designing
From - 5 MVA power T/f LV side
To - 11 kV LA’s
• RMS Symmetrical Short Ckt current = 17.39 kA (As per Tender spec.)
• Fault Clearing Time = 1 sec
• Min. Cable Size = (17.39x1000xsq root 1)/94= 185 sqmm.
• Min. Cable Size = 1-3C 185 sqmm.
• Cable Length = 0.06 Km. (Assumed).
• Ifl = (5000x1000)/(1.734x11000x0.9x0.95) = 307 A.
• Derating Factor = Ca X Cg = .88x1 = 0.88
• Cable sized considered = 3C X 185 sqmm. (XLPE+Al).
• Cable Resistance (Ohm/Km) = 0.21
• Cable Reactance (Ohm/Km) = 0.087
• Cable Ampacity = 330 A.
• Cable Derated Current = 330x0.88 = 290.4 A.
• Min. No. of cable required = 307/290 = 1.0586 = 1 No.
• No. of Cable Runs Selected = 1 No.
• % Voltage Drop = (sqrt 3x307x0.06(0.21x0.9+0.087x0.43)x100)/(1x11000)
= 0.066 % (Acceptable)
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / tariqusman
sorry i remind you that if u determind the above value of
cable size, for example i find 20 sq. mm cble for 83 ampere
load . so u use the 25 sq. mm cable.
sorry for 20 sq mm. there no have 20 sq.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / md. ekram ali
Ye sab galt jawab de rahe hai koi v correct answer nahi diya
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naushad ashraf
As we Now that,
Area= (IscXrtT)/K, Factor for PVC or XLPE,
As we know that Derating Factor = AgXAaXAsXAf
and I= P/(rt3XVXCos#)
and I=DfXI
| Is This Answer Correct ? | 0 Yes | 0 No |
Caliculate the Specific Fuel consumption of 320 kva diesel genarator set?
what is the function of a circuit breaker ?how does the circuit breaker function during normal operation of an electrical system
Wat is power factor exact meaning in terms of technical terms plz explain ?
What is harmonics in AC waves. How it is generated? How it will effect the system network? how can eliminate it?
Using 11000V/433V,3 ph,50Hz,500 KVA, what is the maximum capacity of motor in KW that can be connected and started at a single moment? Also explain about any calculations and formulas used in deriving the same.
What happen if 200KVAR capacitor continuesly connected to load and all the plant machinaries are not in working?
How much inductance or resistance require as a starter in series with induction motor of specific capacity(e.g. 5 hp) ? What is formula for it ?
what is an isolation transformer??? what is its purpose??? what happens if it is not used where it should be used?????
what is green house effect?
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
How do you select a cable size(Cu & Al) for a particular load?
insulators advantage in transformer yard?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)