Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I want formula to calculate cable size as per load given in
kw & amp.I searched many sites but didn't right answer.Plz
reply me asap.

Answers were Sorted based on User's Feedback



I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / engr. abed alraheem

dear you can calculate the size of the cable as follow:

first you need to measure the current capacity and it's low as follow:
Kw/(P.F * Voltage that we wanna use)= current

so when you get the current capacity for the load you can get the size from catalogs there is tables gives you the rating of current and how much the size for every rate for this current.

and this current will be ok if we dont have a voltage drop in line of distance between the source and the load.

actually all the distance between the load and the source have a voltage drop so we have to use this law in order to measure the percentage Voltage drop and it has be 2.5% from the load to panels:

V.D = {((x sin@ + Y cos @) x I x L)/ V } x 100%

I is the current that you measured.
L is the distance between the load and the panel.
V is the voltage that we use.
X is the AC resistance.
y is the AC reactance but sometime we ignore it.
X,Y it is depends on the size of cable so when you chose size this factors will control the voltage drop and you can change it sometimes to get the voltage drop rate as 2.5%

Is This Answer Correct ?    17 Yes 8 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / inudeen

FIRST YOU CALCULATE VOLTAGRDROP
VD=1.732*V*L*I*Z/1000
%VD=VD/RATED VOLTAGE*100
LV CABLE MINIMUM=5%
MV CABLE MINIMUM=3%
V=VOLTAGE
L=LENGTH FOR FEED
I=AMPS
Z=IMPEDANCE

Is This Answer Correct ?    10 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / antony ngigi

What is the correct size of cable[4core armoured cable]for
aload of 15kva.

Is This Answer Correct ?    11 Yes 4 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / anubaby

Voltage drop Calculation for Exaple 2Run cable
=mV/A/M(Full load current/2)length
for single Run
length x Full load current x mV/A/M/1000
mV/A/M find from cable Catalogue
this is only for Voltage drop

Is This Answer Correct ?    7 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / saran

hey hi he needs formula for cable calulation without refer
any catloge

Is This Answer Correct ?    9 Yes 4 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / berialay

i have a load 230 ampere and the length to the MDP is 285
meter the is going to mdp in a pvc duct under ground i need
the formula

Is This Answer Correct ?    6 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / nour travis

Voltage drop works on Ohms Law.Multiply the route length in
metres by the the number of ampers of current that the
appliance draws,and then multiply by the number of milivolts
per ampere metre (mV/A.m)
Formula: Vd = L x I x Vc /1000
Where: Vd is the voltage drop measured in volts
L is the length of the cable in metre
I is the circuit current in Ampere
Vc is the millivolts per amper per metre droped
along the cable
1000 is a correction factor applied because Vc is in
millivolts and Vd is in volts.

Is This Answer Correct ?    37 Yes 33 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / engr wasim khan

Oh Dear..Its so easy...Follow these simple steps (below
link)...

http://www.electricaltechnology.org/2013/10/How-to-determine-the-suitable-size-of-cable-for-Electrical-Wiring-Installation-with-Solved-Examples-in-both-British-and-SI-System.html

Titled as "How to determine the suitable size of cable for
Electrical Wiring Installation with Solved Examples (in both
British and Si System) "

Is This Answer Correct ?    5 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / engr.muhammad younas khan

CABLE SIZING FORMULAS:-
1ST STEP CALCULATE THE VOLTAGE DROP (Vd).
(1 ph.) Vd= 2 x I x L x P.F/(K x Area mm2)
(3 ph.) Vd=1.732 x I x L/(KxArea mm2)
where:-
I:- Load current
L:- Length of the conductor.(in meters)
K:- 58 for copper conductor and 36 for aluminum conductor.
2 for single phase and sqrt 3 for three phase.
____________________________________________________________
2nd step.
AREA mm2 = 2 X I X L /(K x Vd) (FOR SINGLE PHASE)
AREA mm2 = 1.732 x I x L/(K x Vd)(for three phase)
____________________________________________________________
FORMULAS DESIGNED BY
ENGR.
MUHAMMAD YOUNAS KHAN
M.Sc.Engg.,MIEE(UK)
NEAR KEEKER WALI MASJID.
MOHELLAH LAKER MANDI
WAZIRABAD CITY,PUNJAB
PAKISTAN

Is This Answer Correct ?    5 Yes 1 No

I want formula to calculate cable size as per load given in kw & amp.I searched many sites but..

Answer / santhosh

as one of our friend said above
for Al its 1.2 amps and for Cu its 5.0 amps per 1 Sq.mm
but actually its
1 .0 amp for Al and 8-12 amps for Cu [per 1 Sq.mm].

the basic thing is that suppose a cable for load of 100 amps is to be laid then
for Al 100 amps/3 phases=33.33 amps/phases,

as we don't have 33 amps cable take 36 Sq.mm cable (near and above the value) i.e,3 C*36 Sq.mm.
for Cu consider 8 amps for Cu
then 8 Amps*5 Sq.mm =40 Amps per core or phase

i.e,for 100 amps load u need to lay
a cable Al= 3 Core *36 Sq.mm

and for Cu =3 core *5 Sq.mm

Is This Answer Correct ?    4 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

difference between silent and non silent pole rotor?

3 Answers  


Whats the difference between three phase and single phase?

4 Answers  


What will happen if 230V DC motor connected to 230V AC Supply?

15 Answers   Ashok Leyland, BOC, JSW, ONGC, RRB, TRB,


How can we calculate single phase load into three phase load

2 Answers   Jindal, Tanfac,


What is the GNA & MNA in armature reaction of Dc Generator

2 Answers   Khetan,


what is power factor ?

12 Answers   KSEB,


what is ground fault current? is there any current flow takes place through ground? is it possible? if it's possible whether it affect human beings on earth near the fault or not?

2 Answers  


1.Why use in ups in software's,reason,and pls explain. 2.what is the isolation transformer and main use it's functioning and partes.

5 Answers   TATA, Wipro,


What is the difference of grounding and earthing?

6 Answers  


What is the Difference between Power Swing and Out of Step?

1 Answers  


what is the meaning and difference between ELECTRICAL DRAWOUT and MANUAL DRAWOUT?

3 Answers  


How can we decide the fualt levels of sub-stations?

2 Answers   Bhel, Enercon, Prakash Industries,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)