What are the loading factors to be considered for
transformer sizing/selection?
Answers were Sorted based on User's Feedback
Answer / omar aziz
1. Maximum Demand
2. Downstream equipment starting characteristics
3. Total downstream kVA
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / aaman samal
for the selection of transformer the following points are
necessary
1. power demand
2.power factor
3.load factor and types of load
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abhishek robinson
Thermal Loading of transformer
Fault Current
| Is This Answer Correct ? | 2 Yes | 1 No |
one 60KVA UPS how can full load current tell me us formulas
A synchronous machines has higher capacity for (1) Leading power factor (2) Lagging power factor (3) Does not depend upon the power factor of machine (4) None of the above
why number of stator and rotor slots are not equal in IM?
Advantages of short circuit and open circuit tests of a transformer?
At which conditions a synchronous motor acts as a synchronous condenser?
TYPES OF TEMPERING OF ENERGY METER
Why in medium voltage system(3.3kv to 33kv, neutral is earthed with either resistance, reactance or neutral grounding resistance?
What is the drawback of static coefficients?
what is meant by bus bar and outgoing/incoming breaker in an electrical/electronic circuit
how to calculate the conductor size for certain KV transmission line and distribution line?
why secondary terminal of current transformer should not be open circuited?
what is mcb
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)