what will happen if the secondary of current transformer
kept open....
Answers were Sorted based on User's Feedback
Answer / octav
If CT secondary is open then secondary current I2 will be
0, and that lead to I1N1 transforming in heat, and this can
damage the CT; depending on CT range this can be just a
insulation resistance damage or a CT explosion.
Is This Answer Correct ? | 0 Yes | 0 No |
hi raju, great day,
your answer is quite interesting....this is wat am
expecting...but the strange thing is i hav tested a CT in a
open condition (sec) which doesnt given any drastic outputs
lik heating or burning. my CT is 100/5 A in this i hav
given more than 120 A.. do you hav any datasheet for CT.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / gatzrulz
dear max,
i have practically tested the CT with various values of
inputs. but i have n't get any high value of voltage.
Dear Naren,
what you said is wrong. we do have CT's with higher primary
turns and lesser sec turns. Since im in the industrial
field am just telling this.
Feed back is Appreciated
Is This Answer Correct ? | 4 Yes | 7 No |
Answer / r. k.d
Whatever Rajkumar said is totally correct. I like to add
few points in it. when CT is open from secondary side than
it can be assumed that CT secondary resistance is infinite.
Hence, CT will try to increase mag. flex in the core and
when it will cross its rated burden it will get heated and
may explode.
Please remeber that CT will not blow if passes low current.
CT will blow in high current passed for long time only.
that s why CT get blast when short circuit current flows
from the CT.
As open secondary offers high resistance, so it will
produce high voltage accross it.
Hope its clrear.
Is This Answer Correct ? | 0 Yes | 3 No |
FRNDS,
ANSWER 1. INRUSH CURRENT IS NOTHING BUT THE CURRENT
PRODUCED DUE TO THE INDUCED EMF IN THE SEC WINDING. FOR
EXAMPLE IF AT ALL IM USING A 100/5 CT IT IS OBVIOUS THAT
THE INRUSH CURRENT WILL BE VERY LOW COMPARE TO PRIMARY...
ANSWER 2. FRND I KNOW THAT SAFETY ISSUE WILL COME...WHAT IS
IT.THATS MY QUESTION...
Is This Answer Correct ? | 1 Yes | 9 No |
Answer / manfred
The C.T will explode due to the Inrush Current flowing
through the secondary Windings of the C.T
Is This Answer Correct ? | 6 Yes | 25 No |
what is use of thermistor ?
wat's the procedure to take short circuit current for cable selection
How can you calculate in detail the VA burden of current transformer used for Restricted earth fault protection? Please understand that the CT required here is Class PX or X. Also please show the calculations for knee point vtg, stabilizing resistor, magnetising current.
How to design power source say 5KW i/p :415v 3 ph, o/p 5KW constant, variable currnt and variable volatge 10-230v,
when a primary current injection test is required, it is accomplished by what?
What is the Impedance, inductive reactance calculations
In track electrification Either we use single conductor or double conductor? why?
all types of electrical quations
During Load testing of battery charger with temporary AC Generator .When reach 70% load Generator immediately shutdown .we could not able to Recognize ,what is exactly problem .Please kindly clarify us
if power factor comes in leading & showing -0.95. Is there any effect on electrical system? if yes, then please tell me what would be the effects. & how long we keep power factor in leading. Keeping power factor in leading shows more KW & less KVA is it correct or not.
how to avoid electrical shock how capacitor store charges wat are the speed control of induction motors state faradays law flemings left hand rule what is rotary converter wat is transmission and distribution what are the sources of energy abrevation of acb,vcb,sf6,igbt what is output equation of transformer which test copper iron and iron loss are calculated what is eddy current draw a single line diagram (10 marks) draw direct online starter(10 marks)
what is d meaning of inrush current of a trafo ? how u can calculate this ?