what will happen if a cw rotating altenator being
synchronized to ccw rotating altenator
Answers were Sorted based on User's Feedback
Answer / vinodh.t,sil,bellary
both alternators operate in parallel and share load ,for
synchronoisation of two alternators ,we have to check
weather the voltage,frequency,phase sequence,terminal
connection(that is rph of alternator 1 should connect to
rph of alternator2) same.and not the incoming alternators
direction i think....
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jayesh pillai
both alternators are synchronized
so there voltage, frequency, phase and phase difference is
same so they will share load as per there impedances and
kva rating i believe there is no impact if either one is
rotating in clock wise or counter clock wise
| Is This Answer Correct ? | 0 Yes | 0 No |
Differentiate between magnetic field and magnetic flux?
what are the interview question asked in wind mill about electrical
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?
What is the starting current of a DC Motor?
Determine the minimum cable size for a 28A single phase final sub circuit originating from the distribution board supplied by three phase submain. The route length of the final sub circuit is 54 m. Assume 1% voltage drop in the consumer's mains. Submain specification: Cable: 50mm2 4 core V75 copper; Route length 42m; Maximum demand 135A per phase
As we know that during saturation test of CT from secondary side, the current in secondary shoots up after core saturation. How core saturation effects the secondary current?
what is B , c & d curves in MCB characteristics i e Full Form of B , C & D . sir please give me answer
For 132 KV line, PT or CVT which is prefered for measuring & protection? is there any IS or IEE standard available?
What is Nominal voltage?
My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I - is the value of AC fault current. t - is the operating time of disconnecting device in seconds. K – is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.
Why the tank of transformer is made rectangular not circular??
formula for cable size calculation for current?
10 Answers KL Power, ONGC, RL Clean Power Pvt Ltd RLCPPL, SAS, Sobha Developers,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)