what will happen if the secondary of current transformer
kept open....
Answers were Sorted based on User's Feedback
Answer / sripellirajukumar
ya ...this is rajukumar testing engineer...
As per my knowledge ...
it is very important that the secondary of a CT should never
be open-ckted,when the primary is carrying a heavy current.
this is so because
1)if the secondary is open,there is no secondary current and
no secondary flux.The large current in the primary winding
establishes a large primary flux which is unopposed,and this
not only results in huge core losses and excessive heating
of the core,but a high voltage would be induced in the
secondary, this posing a danger to the operator
2)the core gets saturated and
3)the insulation of the windings would be dameged
| Is This Answer Correct ? | 65 Yes | 1 No |
Answer / max
as CT is connected in series, the if the sec side kept open
high value of the current on te primary side will saturate
the core which might be irrversible and in addition voltage
level at sec side will be very high resulting saftey issues
| Is This Answer Correct ? | 22 Yes | 3 No |
Answer / max
dude as CT will step down current value it will step up the
voltage hence on the sec side resulting in very high voltage...
| Is This Answer Correct ? | 25 Yes | 10 No |
Answer / k.narendra
at the primary side the no of turns is less as compared to
secondary, so if we open the secondary the secondary high
voltage at the terminals will exist because we take care
while testing the CT the secondary is closed or not if it
not the person who will at secondary will get effect of voltage
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / simon
Since the primary of a CT uses the strength of the magnetic
field around a current carry conductor to induce a current
in the secondary, it can be said the CT"S act as a source of
current. since V=IR and open circuit on the secondary cause
the resistance to approximate to infinite as a result
extremely dangerous level of voltage are induce in the
secondary, this voltage may even jump across leads. danger
may result in excessive heat causing the device to explore,
as well as electric shock of perssonel.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ayyapss
dear Gatzrulzin ct's primary turns always less than the
sec..In pt's only the turns in the pry is higher than sec.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / ashok
First thing would be explosion of CT. Because of high
voltage generation, it will damage connected metering or
protection relays also.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / sanjay kumar
secondry winding of CT has more no.of turn with less
thickness due to this sec.winding has high voltage with low
current
if secondry winding kept open then sec.voltage will be high
and current zero
high voltage is very dangrous to a person who working near
by & keeping surrounding at high voltage
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gourav
Transformers operate at nearly constant flux. The principle
of transformer states that in order to maintain practically
constant flux the emf induced by primary produces a current
in secondary (if loaded), which thereby opposes the cause
as per Lenz's law. If secondary is kept open, there will be
no opposition to induced emf. The situation worsens if it
is Step Up (CT) as heavy current in primary (load current)
will induce dangerously high emf across secondary leading
to saturation of core as well as hazardous situation for
working personnel.
This can also be explained by B-H curve.
| Is This Answer Correct ? | 0 Yes | 0 No |
why the protection turbo generators is most complex?
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
do we use neutral grounding for resistive balanced load? if we use what happen?
Formula to calculate fault current flowing in the neutral line?
Why star delta starter is preferred with induction motor?
What is ment by KVAR and what are the advantage&dis- advantages of KVAR
How does a digital electronic meter work??????
if we run a 3 phase machine on two phase what will happend??? given answer with solid reason please
What is meant by sag?
IF avr is voltage regulator of genset means why we are giving genset CT sense to AVR ?
is the value of inductance depends upon the evalue of thitha in doubly excited machine?
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)