Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?

Answers were Sorted based on User's Feedback



WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / laxmidhar ,nmiet bbsr

we need,
miliamp source(giving supply to i/p)
i to p converter(pressure signal to control valve)
air supply(for input to i/p and control valve)
multimeter(miliamp check)
small screw driver(for adjust zero and span)
and check

4ma for 0
8ma for 25%
12ma for 50%
16ma for 75%
20ma for 100%

Is This Answer Correct ?    6 Yes 3 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / ramkumar

We can calibrate the Controlvalve by using the mA feeder
(make-DRUCK).while calibrating the I/P using mA calibrator
error occurs adjust Zero and span in the I/P .

Is This Answer Correct ?    4 Yes 3 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / uprabhagaran

MA sourse

Is This Answer Correct ?    2 Yes 1 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / zuheir beilouni

Use a current source to calibrate the I/P converter error ,
but if the error was in the valve , calibrate the valve
positioner using Wallace and Tiernan calibration box or for
fast calibration couple a monostat gauge to calibrate and
if both were ok problem lies in the solenoid then check the
supply to it

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / biju

We can calibrate a control valve by connecting a HART/FF
communicator to the valve and then doing Autocalibration
through the instrument...

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / mustafa ahmad

mA SOURCE & HART COMMUNICATOR WILL USE FOR THE CALIBRATION
OF CONTROL VALVE .WHEN U CALIBRATE THE CONTROL VALVE THAT
TIME U FOUND ANY ERROR . YOU DO AUTO CALIBRATION BY HART
COMMUNICATOR . WHEN AUTO CALIBRATION WILL FINISH , YOU DO
THE STROKE CHEK BY HART COMMUNICATOR OR mA SOURCE

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / dhanasekaran c

Depends upon the valve. Pneumatic calibrator for 0.2to
1.00kg/cm2 Valve.For Electronic positioner( 4-20ma) We can
use Loop calibrator. For Smart type of positioner fixed
valves smart calibrator 275 or 375 or 475(latest) must be
used. Field bus MC5 hand held calibrator can be used.

Is This Answer Correct ?    9 Yes 12 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / antionyo

control valve calibrator

Is This Answer Correct ?    2 Yes 5 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / abinecious

SCANDURA

Is This Answer Correct ?    1 Yes 7 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / janardhan reddy

we can calibrate the control valve by using the dead weight
tester and transmitter and pid controller,

Is This Answer Correct ?    7 Yes 24 No

Post New Answer

More Instrumentation Interview Questions

what is maxdna ?. explain about the software details.

0 Answers  


Can SmartPlant Instrumentation be used in a concurrent engineering environment?

1 Answers  


what are the selections available in configuring a burnout protection of a controller? thanks

0 Answers   NPC Alliance Corporation,


My friend has faced this question! I don't know clearly. So please anyone give me the correct and short answer to this question? What is variable frequency drive? Types, what is star to delta? Why this arrangement necessary?

5 Answers   Asian Paints, TCS,


How to calibration coriolis flow meter?

0 Answers  


Why we not use 2-20Ma or 1-20Ma

5 Answers  


I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME TIME IT IS STABLE. WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY. WHERE AS INDICATION FLUCTUATES. WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE FIELD IT INDICATION IS STABLE. WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE. PLEASE CLARIFY.

5 Answers  


Why in turbine used two critical speed band ?

1 Answers   Ankit Metal Power,


There are two chlorination tonners both are connected to two pressure swithes and the pressure switch is connected to SOV which operates the valve to changeover the tonner selection i.e if pressure one tonner goes low the other tonner should come in line if it is inautomatic selection design a circuit using relays ?

0 Answers  


we have LPG spherical Tank and we want to install DP Xmtr for level measurement.below are the physical measurements Total height of tank is 1850 mtr but 0% level is 1000mm above bottom and 100% level is 450 below upper side.What is the LRV and URV and please mention the formula .The SG of LPG is 0.53 and Wet Leg method will be used.

7 Answers  


why used three wire in RTD.

8 Answers   BARC,


why we use casced loop

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)