Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?

Answers were Sorted based on User's Feedback



WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / laxmidhar ,nmiet bbsr

we need,
miliamp source(giving supply to i/p)
i to p converter(pressure signal to control valve)
air supply(for input to i/p and control valve)
multimeter(miliamp check)
small screw driver(for adjust zero and span)
and check

4ma for 0
8ma for 25%
12ma for 50%
16ma for 75%
20ma for 100%

Is This Answer Correct ?    6 Yes 3 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / ramkumar

We can calibrate the Controlvalve by using the mA feeder
(make-DRUCK).while calibrating the I/P using mA calibrator
error occurs adjust Zero and span in the I/P .

Is This Answer Correct ?    4 Yes 3 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / uprabhagaran

MA sourse

Is This Answer Correct ?    2 Yes 1 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / zuheir beilouni

Use a current source to calibrate the I/P converter error ,
but if the error was in the valve , calibrate the valve
positioner using Wallace and Tiernan calibration box or for
fast calibration couple a monostat gauge to calibrate and
if both were ok problem lies in the solenoid then check the
supply to it

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / biju

We can calibrate a control valve by connecting a HART/FF
communicator to the valve and then doing Autocalibration
through the instrument...

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / mustafa ahmad

mA SOURCE & HART COMMUNICATOR WILL USE FOR THE CALIBRATION
OF CONTROL VALVE .WHEN U CALIBRATE THE CONTROL VALVE THAT
TIME U FOUND ANY ERROR . YOU DO AUTO CALIBRATION BY HART
COMMUNICATOR . WHEN AUTO CALIBRATION WILL FINISH , YOU DO
THE STROKE CHEK BY HART COMMUNICATOR OR mA SOURCE

Is This Answer Correct ?    0 Yes 0 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / dhanasekaran c

Depends upon the valve. Pneumatic calibrator for 0.2to
1.00kg/cm2 Valve.For Electronic positioner( 4-20ma) We can
use Loop calibrator. For Smart type of positioner fixed
valves smart calibrator 275 or 375 or 475(latest) must be
used. Field bus MC5 hand held calibrator can be used.

Is This Answer Correct ?    9 Yes 12 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / antionyo

control valve calibrator

Is This Answer Correct ?    2 Yes 5 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / abinecious

SCANDURA

Is This Answer Correct ?    1 Yes 7 No

WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?..

Answer / janardhan reddy

we can calibrate the control valve by using the dead weight
tester and transmitter and pid controller,

Is This Answer Correct ?    7 Yes 24 No

Post New Answer

More Instrumentation Interview Questions

If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?

5 Answers  


why the steam drum and deaerator level transmitter range is in negative MMWC to zero

3 Answers   Emerson, Jindal, JKPM,


How to connect another 24 volt dc power supply in circuit when previous power supply has become weak.what is the connection?

2 Answers   Bhole Baba Dairy Industries,


when we are using HART COMMUNICATOR why we are using 250 ohm resistance while using HART COMMUNICATOR.

7 Answers  


Definition of level

3 Answers  


how many type conductivity sensor ?

0 Answers   Process Automation,


What are the logic behind 2x2 and 2x3 logic and more when ask in interviews

1 Answers   Reliance,


Why plc require in analog input 4-20amp & 0-10 volt?

0 Answers  


I am manjunath having exp in maintenance of chemical plants,know i want to do a design course INTOOLS,after doing design course can we get jobs in design field.sinve i dont have design exp..

0 Answers  


How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error

2 Answers  


why 4 to 20 ma ,why not 0 to 20 or 3 to 15 or anything

19 Answers   Honeywell, TCS, TN,


hi! i want to know about mpse exam.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)