what is mean by hot loop and cold loop testing, whts
different between both
Answers were Sorted based on User's Feedback
Answer / mrmk
Cold Loop checking: Checking of wires continuity of
respective field instrument-Junction box-DCS/PLC
marshalling panel terminal.
Hot loop checking: Once you powerup your field instrument
through DCS/PLC system, by stimulating process input from
respective field instrument and cross check its responce at
DCS/PLC sytsem
Is This Answer Correct ? | 156 Yes | 6 No |
Answer / gray
Following the IEC guidelines (62382), there is no such
thing as a cold and hot loop check.
There is a wiring/ point to point that all should do before
carrying out a loop check from field device to DCS display.
Is This Answer Correct ? | 7 Yes | 29 No |
1)How many tpes of vibration probe and how many tpyes of vibration. 2)how we can calibrate a vibration probe with tk3 3)what is RMS value in vibration measuring application and how we calculate it.
why most of the DP transmitters using maximum range as 0-2500mmwc?why not 1000 2000 3000 4000mmwc
Can anyone help me with the Question bank(objective type) for complete Instrumentation engineering,either a soft copy or a Hard copy(Book),or the name of the author ,or publisher.
how many type of plug are used in pneumatic control valve,name them.
why we are using 4-20ma why cant we use 4-40ma
In RS 500 SLC 5/03 input change one module card to another card, plz. give steps clearly.
Explain what is meant by the term “FLASH POINT” of liquid?
How many are the types of instrument cables in terms of No. of pair.
while i check zero check for dp flow transmitter some fluctuating came (0 to 458 kg/h) what is the reason?
i want to know for good instrument engineer or success how many software knowledage required & from which university
what is proportional & what is proportional band
In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...