Furnace draft transmitter range is -50 to +50 mmwc. why the
impulse line connected in hp side?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
A draft range measurement is typically a gauge pressure
measurement, referenced to atmosphere.
Draft range is very, very low pressure, so DP transmitters
are typically used because they're readily available in
a 'draft' range with the large diaphragms necessary for low
pressure measurements.
The high side is connected to the process with an impulse
tube. The low side is exposed to atmospheric pressure.
Good practice puts a filter, like a scintered pneumatics
filter on the low side, so that dirt doesn't fill the low
side cavity and air movement (wind, passing vehicles) is
buffered and damped to prevent the forces of air movement
on the low side from affecting the draft measurement.
If the impulse line were connected to the low side, the DP
would be negative, a DP subtracts the low side pressure
from the high side pressure (atmosphere minus some positive
pressure = negative pressure). Convention says that draft
range is positive so the impulse connection is to the high
side, to get a positive value.
Tell 'em Carl sent you.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / deepak
Dear Carl,
Cant we use an Absolute pressure transmitter ?
Is This Answer Correct ? | 1 Yes | 0 No |
how can we calibrate the differential pressure transmitter by using HART communicator
why we use condesiate parts before tranmitters?
what is pt100 RTD, and does 100 stands for
what is formula mv convert to temperture
what is the difference between 3,4 wire RTD sensor?
6 Answers HTA Instrumentation,
I HAVE PRESSURE TRANSMITTER WITH TWO WIRES 24 VOLTS SUPPLY.IF TRANSMITTER WILL GIVE SIGNAL TO THE DCS WHAT HAPPEN TO THE 24 VOLTS POWER SUPPLY IT WILL DROP OR REMAIN TO 24 VOLTS POWER SUPPLY.
If we increase only P what will be controller action ?
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.
The wire is disconnected from the temperature sending unit (magnetic gauge). A voltmeter connected to the wire reads 0v. What does this indicate?
A pressure Tx accuracy is 0.2%. Signal o/p is 4-20ma.span is 16 Ma.how many deviate the o/p then calibration needed
i hav applied for the post of engg. in iocl so please require the past test papers fro instrumentation engg please please help me and send me the papers or tell me the pattern and type of ques asked in examination......
How the sizing of the analog signal cable is calculate?