WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
Answer Posted / laxmidhar ,nmiet bbsr
we need,
miliamp source(giving supply to i/p)
i to p converter(pressure signal to control valve)
air supply(for input to i/p and control valve)
multimeter(miliamp check)
small screw driver(for adjust zero and span)
and check
4ma for 0
8ma for 25%
12ma for 50%
16ma for 75%
20ma for 100%
| Is This Answer Correct ? | 6 Yes | 3 No |
Post New Answer View All Answers
What is megering????
What are the types of valves?
How to regulate the flow of Air in 4" line, with max flow of 330 nm3/hr and Pressure of 0.5 bar? please suggest the type of instrument required.
describe flow nozzel principle?
what will the sending unit in the fuel gauge utilizes?
what is the advantage of submersible level transmitter compare to ultrasonic level transmitter?
How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer
Question on maha cement
please any body have most important data for study for saudi aramco test of instrument QC thanks email shahnaveedullah@gmail.com
Programmable Logic control.
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.
I have completed B.E. Instrumentation & control in 2009. i have 3 year industrial job experience in chemical plant.now, I want to join M.E. in external. so, Plese say easiet way and good institute name.
Calibration procedure for water rotameters
can you provide me full detail about instrumentation in ONGC??
Can any one send me IOCL instrumentation question papers.. i dont know the pattern of the questions and what to prepare can any one help me on this .. my email id is anwarnishil@gmail.com