In dcs contol valve parameters showing like this
Gain=1 or 2 , ti=7 sec, td=20sec. But temp,pressure,level control valves we are using in which type parameter side using ti,td clearly tell me
Gain, ti and td are PID proportional control tuning terms/constants. PID controllers use PID tuning constants to calculate an output based on the error signal; final control elements (valves) do not do a PID calculation so valves are not involved with gain, ti and td. The controller is typically in the control room, the valve is somewhere out in the process.
A PID controller calculates the expected valve/damper position from the error signal and the tuning constants, the result of which is an output control signal ranging from 0-100%.
A valve positioner or valve I/P receives that control signal from a controller (4-20mA, Profibus) and supplies air or electric power to the actuator to achieve the correct position demanded by the control signal.
Ti is the term for reset or integration. It is used when the process itself is not an integrating process. Level, pressure, and pH are usually integrating processes. Sometimes temperature is an integrating process, sometimes not. When the process is non-self regulating/integrating process, the ti term is not used in the PID calculation.
Flow and temperature processes typically use the ti term for PID calculation.
An exception to the rule of PID being done in a separate controller is Foundation Fieldbus (FF), which allows function block PID execution in FF devices. In a case where PID control is executed in an FF valve positioner, then a valve would use the PID tuning constants.
| Is This Answer Correct ? | 4 Yes | 0 No |
warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?
What are the application of bernoulli’s theorem?
How d.p. Transmitter can be applied to close tank?
HOW THE ORIFICE & PRV SIZING BE HAPPENED -- EXPLAIN IN BRIEF
Where do we consider the pressure in mbar & where do we consider the pressure in bar & why is it so ?
2 Answers BOC, Jindal Steel and Power,
what is the input of ph sensor and meter during the calibration time and what is the output?
selection of the zener barrier for the hazardeous area zone 0
HOW TO DO PERFECT CALIBRATION OF DIFFERENTIAL PRESSURE TRANSMITTER FOR CLOSE VESSEL TANK LEVEL PURPOSE ???? AND HOW TO MAKE ZERO PRESSURE ?? Rosemount 2051 Pressure Transmitter with HART® Revision 5 and 7 Selectable Protocol BIENG USED !! HOW TO CALIBRATE FIELD SIDE DPT WITH THE HELP OF SPAN & ZERO PUSH BUTTONS ??
my data card only does run in my mobile so how can change it that it run other mobile & computer and i can stor data in my data card
how can check the loopchecking for valves?
i have level transmitter -400 to 0 range for steam drum application but i am unable to calibrate if installation of lt below lower tap what will be the effect ? and as per std wht is location of lt ,above lower tapping or below
What is safety barrier and how it is work
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)