How can calculate ups battery back up time?
Answers were Sorted based on User's Feedback
Answer / g.shanmugam
Battery back up time=Battery current at full load/Battery Ah
| Is This Answer Correct ? | 308 Yes | 161 No |
Answer / guest
As a thump rule,if we need 1 hrs backup from the 1 KVA UPS
12V/130AH is Required,For Example,10 KVA ON-Line
UPS,Battery-12V/65AH,26 nos.
BAck-up Time=Ah of the Battery*Total no of the
Battery/Output KVA*130
BAck-up Time=65*26/10*130
BAck-up Time=1.3
BAck-up Time=60~70 Mins(Approx)
| Is This Answer Correct ? | 219 Yes | 147 No |
Answer / r.gopalakrishnan
SEE SUPPOSE IF I NEED 740 WATTS USAGE BACK UP TIME UP TO 3
HOURS, THAN I CAN CALCULATE LIKE THIS(EXAMPLE 1
PC@350WATTS,3 FANS@80X3=240WATTS& 3TUBE LIGHTS
@(40+10CHOKE)=50=150WATTS)TOTAL=740 WATTS REQUIRE,= 740
DIVIDED BY 12 V=(61.666667)>61 Ah per hourx3
ours=183Ahbattery,(180Ah Battery).now you have selected
battery & than select a UPS/inverter that is you can only
get 80% of your UPS/inverter.Ex;1000 watts Ups/inverter.that
will be always safe for you & ever.thanks.R.GOPALAKRISHNAN.
| Is This Answer Correct ? | 96 Yes | 40 No |
Answer / sss
UPS Backup=Battery Voltage*Battery Ah/Load (watt)
| Is This Answer Correct ? | 98 Yes | 47 No |
Answer / subir kumar manna
UPS BACKUP TIME= NO OF BATTERY X AH OF BATTERY /OUTPUT KVA
X130
| Is This Answer Correct ? | 66 Yes | 41 No |
Answer / parameshwara.s
Tell me on a 5 KVA UPS with 12 Batteries of 65 AH how many
hours of backup will I have on full load.
| Is This Answer Correct ? | 36 Yes | 11 No |
Answer / n.muthukumar
ups backup time=battery AH*battery efficiency*no.of
batteries/ups capacity in kva*130*output power factor
for example:65*0.9*10/5*130*0.8=1.125
approximately:1hr 15min
| Is This Answer Correct ? | 39 Yes | 21 No |
Answer / claudiu
You can calculate the max time to use a UPS with this
formula
T max = efectiv energi / average power of the energy
that min
T max = 1377 (this is a constant, it's so big because it's
calculate in seconds)* capacity of batery in volts 12V *
capacity of batery in amper's 10Ah or other valu * number
of moduls (number of bateris to use) / how mutch power you
want to consum in W
for exemple
I have 8 baterys with 12V and 10Ah and I want to standup a
computer with 300 W consum
so
1377*8*10*12/300 = 4406.4 seconds that min 4406.4/3600 =
1.2h
sorry for my english
best regards,
Claudiu from ROMANIA
The sours is
http://en.wikipedia.org/wiki/Uninterruptible_power_supply
| Is This Answer Correct ? | 29 Yes | 16 No |
Answer / asela
nomber of battery * battery voltage * each battery AHR
(130AHR total/ nomber of battery)130/260* efficiancy 90
PERCENT/ tatal VR.
26*12*5*0.9/1000
1 HR AND 4 MINUTES
| Is This Answer Correct ? | 38 Yes | 27 No |
Answer / yogesh
UPS backup time= Ah of battery * no of battery/output kva * 130
| Is This Answer Correct ? | 73 Yes | 68 No |
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
what is the operating time for LBB and how does the LBB relay realise whether cb is opened or not?
What is ac and dc drive.
how work a harmonics filter(L-C combition).
what are the difference between protection class CT and Class PS CT
How to identify the whether its an isolator or Breaker in MDB
what is the excess air in furnace
Why we use parllel operation of alternator
what are the functions of power modulator?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
For a spring controlled governer the relation F = ar+b (F is the controlling force, r is the radius of rotation a and b are constants), indicates that the governer is
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)