what are the types used for alternator earthing,what will
happen if more than two alternator is working in
parallel with each having own system earthing.is there any
possibility for circulating current in between two system.
Answers were Sorted based on User's Feedback
Answer / prw
The earths of each alternator must not be connected at the
same time because this will result in third harmonic
current flowing causing excessive heating. The earth should
be switched so that only one earth is connected to ground
| Is This Answer Correct ? | 17 Yes | 1 No |
if two alternators running parallel and both alternators
neutral grounded by one earthing strip, there is chance of
circulating current. because the unbalanced current flow
through the neutral of one alt.to second alt.by the neutral.
if both alternators earthing is separate , then no chance
of circulating current.
| Is This Answer Correct ? | 13 Yes | 6 No |
the two types of earthing is used: 1. pipe type earthing
2. sheet type earthing
NOTHING WILL HAPPEN WHEN TWO ALTERNATORS ARE WORKING
PARALLEL WITH EACH HAVING ITS OWN EARTHING.
NO THERES NO POSIBILITY OF CURRENT CIRCULATION.
| Is This Answer Correct ? | 7 Yes | 12 No |
various transmission tower like .,D tower ,K.C.O tower ,C.C.O tower,K.C.R tower ,C.C.R tower ,H.C.O tower in different tons.
Sir I want questions for rrb sec technician gr III (electrical)
how to select proper cable for ct wiring so that drop within the limit.
calculation of lad carryinc capacity of 6mm2 cross section wire in 415 voltage circuit. What will be the amps.
what is meant by transformer?
why do we connect voltmeter in parallel,why not in series,and why do we connect ammeter in series why not in paprallel...
WHAT IS A COLOUR CODING OF 3 CORE CABLE
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
how can we calculate the reactence of the current transformers?
What is CVT and what is relation with wave trap?
what is the purpose of high speed earth switch in gas insulated substat
How a synchronous generator practically work? what is the function of avr(automatic voltage regulator)in synchronous generator?how the connection of avr to the generator made practically?please give me the answer.
6 Answers Accenture, Heineken,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)