in a induction motor if we put capacitor across it will the
power factor of the motor will improve? if yes how
Answers were Sorted based on User's Feedback
Answer / preet
IM takes current acting as inductive load from mains,so it
will draw lagging bars from supply and current will laggs by
voltage but other side capacitor delivered lagging bars to
line work as compensator
due to lead current of capacitor and lagging current of IM
resultant will be decrease in V&I angle or improve in Pf
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / kushal trivedi
capacitor bank acts as a reactive power generator. If we
install capacitor bank across the IM,the reactive power
required by IM is supplied through capacitor bank for the
generation of magnetic field,So for a same power delivered
to IM, the value of active current is more so Angle is
Reduced and PF improve.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / gunasekaran
It compensate lagging power factor. motor is inductive load
inductance alway oppose changing current so it is always
lagging with voltage but capacitor always oppose the
changing volage so it always leading PF so this compensate
the lagging reactive power.so active power consuming from
source will be reduced for given load.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / hardik vyas
It depends how is it connected. normally for 3-phase motor
a three phase capacitor bank is connected as a load with
across motor which in turn improves the power factor of
system.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / manish singla
Connecting capacitors in parallel to induction motor does
not necessarily improve the Power Factor. There will be two
cases as listed below;-
If motor is already running on full load then itself its
power factor will be in the ranges of .85 to .9.
If motor is running without load i.e. Idle, then there will
be lot of scope in improving power factor by connecting
Capacitors in Parllel.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / master ramunniraja
Yes, Motor is a inductive load, it generate lagging PF. If
we use capacitor PF will increase because capacitive load
generate Leading PF. So Both are compensated So PF increased.
| Is This Answer Correct ? | 0 Yes | 1 No |
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
What is the value of 3 phase voltage?
what is the merz prodution ? what is the turn to turn fault?
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
Which capacitor is preferred for high voltage and frequency?
WHICH IS BETTER( FOR POWER SAVING)- ON LINE OR OFF LINE UPS ?
3 Answers Punjab National Bank,
How to select the ratio of neutral ct? Is there any relation in between percentage impedance and neutral ct ratio ?
what is pmu
Explain the role of a car driver as one of a feedback mechanism.
Why we are using Isolation Power Transformer inplace of commercial power transformer? What's the difference between them?
CPC cable .PVC \1C....I want to get sure that type is flexible indoor or to be install on trench. please advice .thanx :)
what is the highest transmission voltage in India till now?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)