A 3 phase motor operating off 415V system is developing 20Kw
at an efficiency of 0.77 and power factor of 0.73.
determine:-
a)the line current.
b)the phase current if winding are delta connected.
c)the phase voltage if winding are star connected.
Answer / v.srinivas
I=P/1.732 X 415 X EFF X PF=49.5(LINE CURRENT)
28.57 AMPS (PHASE CURRENT)
Phase voltage in star connection; 718.78
| Is This Answer Correct ? | 0 Yes | 0 No |
What tests should i carry over on a newly rewinded DC Generator with voltage rating of 38 volts and current rating of 350 amps, to certify that the machine is OK?
in transmission line, if the load is suddenly increased at the receiving end of the system the phase shift will (a)decrease (b)becomems zero (c)increase (d)not be affected
How to select the Cable size for 550 Amps Load without seeing the cable Catalogue?
What is the ratio of Booster transformer?
which INDIAN STANDERD in Mention the earth test value?
What do you mean by pf of a generator? Power factor purely depends on the load (wether inductive, reactive or unity) then what does the pf mentioned on the generator nameplate means?
what is corona
WHAT HAPPENS IF FUSE IS CONNECTED TO NEUTRAL WIRE
Difference between HRG and NGR. Are they both the same thing
Single line diagrams for star to delta and DOL starters.
How to calculate the 2500 Kva Transformer losses Primary 11KV Secondary 415volts
For high voltage and low current Circuit Breaker preferred is vacuum circuit breaker.why?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)