If DC supply is given to a transformer it may
a) Work
b)Not Work
c)Give lower voltage than the rated voltage on secondary
side.
d)burn the winding
Answers were Sorted based on User's Feedback
The Transformer is working based on the principle of mutual
induction(M) between primary and secondary winding.
(M = L. dt/dI). This induction comes due to the magnetic
flex produced by AC supply.
In DC, No meaning of flex. So induction between two
windings is not possible. thus when we are giving DC supply
to Primary winding, It act as a normal conductor.
Due to copper loss of the winding, the heat will increases
and this will affect the winding including insulation
strength.
Is This Answer Correct ? | 35 Yes | 1 No |
Answer / baljinder singh
First of all ,when we give the dc supply to
transformer,flux set up around the winding or in core ,but
this flux is statoinary and not link with winding so there
is not produce the back emf .The resistence of primary is a
few ohm(1-5).According to ohm law I=V/R .
When voltage applied across ,the back emf is not
produce ,resistence is very low ,so heavy current flowing
throw it .The winding will burn.
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / ramesh molli
T/F WORKS ON THE PRINCIPLE OF MUTUAL INDUCTION. BUT IN DC
THERE IS NO MUTUAL INDUCTION, SO T/F NOT WORKS ON DC SUPPLY.
Is This Answer Correct ? | 8 Yes | 7 No |
Answer / puja sinha
b)it will not work.because a transformer works on the
principle that an alternating flux is produced bya an
alternating quantity that oppose the main field.if the
supplied quantity is not alternating <alternating flux is
not produced and the transformer will not work.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / puja sinha
b)it will not work.because a transformer works on the
principle that an alternating flux is produced bya an
alternating quantity that oppose the main field.if the
supplied quantity is not alternating <alternating flux is
not produced and the transformer will not work.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek
d)burn the winding
Ans-If we apply dc supply across the transformer primary side,there will be no pulsating or alternating flux in the transformer core.Hence there will be no mutual as well as self induced emf as the flux is not a time varying one.As there is no self induced emf in transformer primary,there will be no back emf and as transformer primary resistance is low,there will be a high current in the primary side.Hence high copper loss and it will damage the winding insulation.
Is This Answer Correct ? | 0 Yes | 0 No |
why we use 3 phase in our country?..why no 4,5 or 2??
I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions
In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
IN A HT CABLES i.e. 1.9/3/3 kv, what is the meaning of 1.9 and 3.3.
what s the differenc between electrical &electronis , how to define them
why power generated only 11KV not more than???????? and why power up/down is multification of 11*?=??.??? foe Example 11/33,11/66,66/11KV etc,
which type of effect of turbine and generator reverse power protection ?
give me atleast four differences between circuit and network
Why mostly GT(Generating Transformer)has only Ynd1 Vector Group?
In LT Line What is the minimum clearance required between phase to phase busbar & between Phase to body of the panel? Also between Neutral &phase, & Neutral & body of panel. as per standards.
In Electrical 'Single Line Diagram' cable nomenclature shows "2 X 1C X 630sq.mm to be provided for one incomer. The question is how many cable to be proved for one Incomer.