Why we use series reactor in power system?
Answers were Sorted based on User's Feedback
Answer / sunil
series reactor is used to limit the fault current. b'cos
reactor contains inductance and it opposes the rate of
change of current
Is This Answer Correct ? | 44 Yes | 3 No |
Answer / niaz ahmed bijapure
to limit short circuit current
to reduce 1 2 3 harmonic
to reduce inrush current
to increase inductance , reflectance of circuit
Is This Answer Correct ? | 26 Yes | 5 No |
Answer / sibasish
to limit short circuit current
to reduce 1 2 3 harmonic
to reduce inrush current
to increase inductance , reflectance of circuit
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / mangesh karande
To limit short circuit currents and thus to reduce fault
MVA. Also to keep to sources permanantly parallel.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / som
It is installd 2 cmpensate
inductive VAR and stable the
voltage profile in receiving
end side.
Is This Answer Correct ? | 11 Yes | 10 No |
Answer / shravan kasaudhan
For reducing the scc(short circuit capacity).
Then faulty current will be reduced and size of switch gear will be reduced I.e.cast of switch gear equipment is no more
Is This Answer Correct ? | 0 Yes | 0 No |
in HT service 3ph 4 wire service Y-phase voltage shows zero . whether it is meter fault? or what be the reason ? if y-ph voltage zero ,can current is recorded? reasons for failure?
What is the advisble power factor to be maintained in grid connecting power generation plnats without any effecting the generator.
Whether capacitor loads can be connected for testing a diesel engine at its full load capacity? Is there any limitation of capacotir load? Which is the best load for testing DG sets?
why celing fan is running in anti clock wise and table fan is running in clock wised?
WHAT IS THE COOLANTS IN TRANSFORMER?
1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
16 Answers Ecil, Engineers India, MahaDiscom,
Please provide me detail cable voltage drop calculation
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?
What is the Diff. btw Fire Alarm System & VESDA System??????
Explain what happens to the speed of a series motor as the load decreases
Why we use parllel operation of alternator
do we convert single phase line to three phase at minimum cost?