how to calculate the megger values for motor, cables and
transformers?
Answers were Sorted based on User's Feedback
Answer / karan
The thump rule is voltage rating +1 example for a 11KV
motor it should be 11+1=12 Mega ohm.
In addition to that the PI is the ratio between 1Mnts and
10 mnts.It should be above 1.5
For examle IR at 1mnts= 10M.ohm,
IR at 10 Mnts= 20 M.Ohm
Then the Polarisation index is 2 which is consdierd
good.When it is below 1.5 you can heat the tranformer or
motor then the value will come up.
Is This Answer Correct ? | 25 Yes | 4 No |
Answer / priyan
see sundar
Meggering test is done for any electrical equipments to
find the insulation resistance value.
As per the standards for testing the machines 3 methods are
there
1)spot reading 2)time-resistance testing method 3)step
voltage test
the following is the second mehtod it is in use nowadays
PI=10 min/1 min value
Then the Polarisation index is 2 which is consdierd
good.When it is below 1.5 you can heat the tranformer or
motor then the value will come up.
Is This Answer Correct ? | 15 Yes | 4 No |
Why machine give shock
what are the safety measures of induction motor?
why should the lowest unit of a testing transformer ( cascaded transformer ) have higher power rating??
how to test reverse power trip?
what is bausbar?
What is the pro & con of having 11kv & 33kv incoming, and what is the adv & disadv. of converting from 11kv to 33kv.
what is buscoupler adopter panel????
what is the function of a commutator in a dc generator?
14 Answers College School Exams Tests, NTPC, TCS,
minimu size and length of gi earth pipe
How to measure the Harmonic Distortion of UPS ie THD?
when we increase load , current drawn from source also increases why ?
How do we calculate over and under frequency tolerance from generator data?