The thump rule is voltage rating +1 example for a 11KV
motor it should be 11+1=12 Mega ohm.
In addition to that the PI is the ratio between 1Mnts and
10 mnts.It should be above 1.5
For examle IR at 1mnts= 10M.ohm,
IR at 10 Mnts= 20 M.Ohm
Then the Polarisation index is 2 which is consdierd
good.When it is below 1.5 you can heat the tranformer or
motor then the value will come up.

Is This Answer Correct ?    25 Yes 4 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Give details on how you intend to handle a challenging position you are posted to manage unexpectedly as a company staff?

2892


Why does increasing the magnetic flux in the main field of a d.c motor cause the armature current to reduce??

1523


what is the difference between interconnection and intraconnections in the circuit diagrams

7570


what is through fault?

1770


A 10 MVA, 66KV, 50Hz, Y-connected 3-phase alternator has synchronous reactance of 0.635 Ù. It is working at full load at 0.8 lagging p.f. condition. Find torque angle, neglect armature resistance.

2088






Can any one give an explanation about rating factors of cable? if we are laying the cable on the air with an temp 15 degree then rating factors will be 1.15 and if we are laying the cable on the air an temp 60 degree then rating factor will be 0.76 please describe it and what is the difference between rating factor and derating factor?

1043


why transmission is only 3 phase and not 2 or 4 or poly phases

1712


what is the difference between neutral and earth

1562


what are the ''pitting rings''and how cn they be controlled in a series generator

1372


internally connection of photvoltic module

1463


What is the lockout relay

1071


What is the minimum IR value of HT/ LT cable? Pls post separetely!!!!!

1950


What is the difference between single point and double point bonding. please kindly detail about bonding of cables.

1923


What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw

1419


percetans

1713