say a transformer is designed for 33/11kv step down with
ratio 0.33 for load 1 mva. if am giving 11kv as a input
that same transformer what will happen to its o/p voltage.
and whether it can be operated for 500kva
Answers were Sorted based on User's Feedback
Answer / ankamsreekar
the current rating on 33kv side with full load is 30.30 in
case of 1ph transformer. if we apply 11kv to 33kv side the
transformer rating will be 333.33 KVA insted of 1MVA.the
voltage will be 3.66kv.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
The iron losses are reduced to nearly 33 %.As the tr
capacity is based on 'cooling vs heat generated',the
capacity can be higher than 333.33 KVA.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / reza
The trans act whit no happen.But we must use from reduced
load.
| Is This Answer Correct ? | 0 Yes | 0 No |
why Line voltage =1.732XPhase voltage what mean by 1.732
What is AMF Panel????
What is ramp signal?
WHAT IS THE TOTAL POWER GENERATION IN CHHATTISGARH?
why vaccum circuit breakers are preferred over m.o.c.b
1> what r different types of fault in cables? How will u locate and test these faults? 2> why earth wire is provided on top throughout the transmission line. why not only on towers? How much area it can protect? 3> what r different types of transmission losses? How power loss can be minimized? 4> what is the % of power loss on transmission lines?
dear all, can any body explain that how to select an induction motor for a specific mechanical load(inertia). is there any formula or calculation then please give me. i shell be very thankful to all of you. Thank,s and Rgard,s.
How to calculate amount of copper used in a motor (AC&DC), generator and transformer? Datasheet provides power rating and mass of the equipment....can we somehow use this available info.
what is the value of current as well as voltage upto which we will not feel shock and why?
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
in 400 kv system why should trip both side CB when we give hand trip?
In power generator sets, when they are coverted from 50hz to 60hz, the kva rating after conversion increases. For example, the manufacturer of a perkins 200kva @ 50Hz generator set has mentioned it to become 220kva after converstion to 60hz. What is the relation between the frequency & the KVA rating. Any formula please.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)