Answer / sak
it is not necessary to charge the battery always, instead it
should be charged fully once and after discharging you can
charge it again, as nobody knew till what level it is
discharged. so its better to keep the UPS on charge
continously. Anyhow battery last for maximum a year only.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / rajeshsan
In case of power plants all emergency loads are connected through UPS. So it is very necessary to keep the Battery in fully charged condition.
However, the battery should be discharged and charged to get maximum life.
It was recommended by Battery manufactures to do the charging and discharge the battery atleast trice in year.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amarnath
Its always necessary to charge the UPS its in the case of
Invertor we can charge it after the full discharge
| Is This Answer Correct ? | 1 Yes | 0 No |
how much current does 3ph a.c & d.c motor drawn.Plz. provide formula with example.
define transient state &steady state
What are the Return ( Monthly / quarterly/ Annual submitted to Electical Inspector for an establishment (Factory in Maharashtra-- Small scale category having seperate HT line of 22KV ) as per Maharashtra Electricity Act
why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
7 Answers HCIL, Jindal, Siemens,
-What shall be short circuit current of LV switchgear for a 1000 kva, 11.415kv, 3 phase tranformer with 5% reactance.
What is APFC Panel????
how to calculate voltage drop in long distance cable? for an e.g lamp of 12 volt ac ,300watt is 90 meter away from supply i.e (x'mer 230 v / 12v)and i m getting 8 volts at lamp terminal ....
What is the feedback in the control system?
Can any one help me how to set an overload set the range from 2.8A to 4A , rated motor current 22A, CT 60/5A
what is the meaning and full form of AYFY CABLE?
10 Answers ABB, Cable Wireless, Ecom Associates, Tamboli Engineers,
what is brushless alternator?
How to connect a Restricted earth fault relay for 2000KVA,11/0.433 KV Distribution Transformer and What is the neutral CT ratio should be selelcted for 2000 MVA Transformer for estabilishing the Restricted earth fault relay
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)