is it necessarry to charge the battery of ups always??
Answers were Sorted based on User's Feedback
Answer / sak
it is not necessary to charge the battery always, instead it
should be charged fully once and after discharging you can
charge it again, as nobody knew till what level it is
discharged. so its better to keep the UPS on charge
continously. Anyhow battery last for maximum a year only.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / rajeshsan
In case of power plants all emergency loads are connected through UPS. So it is very necessary to keep the Battery in fully charged condition.
However, the battery should be discharged and charged to get maximum life.
It was recommended by Battery manufactures to do the charging and discharge the battery atleast trice in year.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amarnath
Its always necessary to charge the UPS its in the case of
Invertor we can charge it after the full discharge
| Is This Answer Correct ? | 1 Yes | 0 No |
Logic using 1 kV or 1,1 kV grade in house wiring Low voltage cable. Explain/suggest? some use 1kV and some prefer 1.1kV grade insulation low voltage cable why??
How Many Safety of Transformer
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
why fractional pitch winding generally used in alternators?
what is negative phase sequence
what is the voltages using in movie theaters??? why ??why not other??
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
we have require a Motor (1500kW, 6.6kV, 50Hz) which shall operate at 1500rpm during 30min and after it shall run on 500rpm during 15min. The same cycle shall be repetitive during the whole working days. Which method is best and economic to achieve such type of task. VFD, VVFD, Pole changing motor etc.
11KV electrical line going through the forest in cloudy night ,how can we find the direction of line.
5 Answers Bhel, Cesco, HZL, Nesco,
ult of expression 'document.FrmQF.myem
what is the formula to calculate kva genset required for a given load in kw.
what is the maximum permissible limit value of leakage current and leakage counter reading to replace lightining arrester?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)