what is different between buchhoz relay and pressure relife devices in transformer
Answers were Sorted based on User's Feedback
Answer / ashish patil
For Operation of buzzolz relay it required loe liquid level
& formation of gases which can operate float,but in case of
PRD it required pressure with high capacity then PRD operate
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek goyal
when the short ckt or any other fault happening into the
transformer it will detected by the buchhloz relay (gas will
accumulate into the relay). if pressure into the tank is
above the set point of PRD/PRV it will activate. both are
safety device one can sense the gas other one can sense the
pressure.
Is This Answer Correct ? | 0 Yes | 0 No |
how to synchronize 3 phase slip ring induction motors of different ratings.
typical per KM resistance values of ACSR DOG conductor for 33KV & 11KV OH system? typical per KM resistance values of XLPE 300Sq mm cable for 33KV system? typical per KM resistance values of XLPE 185Sq mm cable for 11KV system?
11KV electrical line going through the forest in cloudy night ,how can we find the direction of line.
5 Answers Bhel, Cesco, HZL, Nesco,
Is there any scope for an electrical engineer in MRF company......
how the speed of the gets motor regulated. does it draw the same current on the all speed level.
watt meter have 4 terminals what there name??? and what theses 4 terminals indicates ?? and why 2 terminals are short circuited??
why power of fm is weaker than am?
May I know how much values to be set for earth fault, over current and short circuit values at 11kv side? I have 11kv van 1250amps rating. Present it's taking load 80amps?
Pls tell me what is the exact current conducting capacity of copper and aluminium cables?how much capacity of cables need to 90kw induction motor&how?
We have a 1275KVA existing Transformer in a power plant project. Customer want to get it test & confirm whether it is a Dyn1 Transformer or not. Pleae let me know how to test it.
BRIEF ME CHECKING PRCEDURE OF BATTERY 12V 26AH
How can we deside Short Ckt level of electrical System,Breakers etc.please provide formula to find SC of HV side & LV side