Two CTs 1600/1 and 35/1 are in series. while checking the
ratio test of a CT(1600/1),same 1600A will also pass
through the CT having ratio 35/1.
Will it be harmfull to the ct(35/1),if yes , what will
happen.CT secondary is shorted
Answers were Sorted based on User's Feedback
Answer / ullas
if 1600 ampere current is passed through the second ct
having turn ratio 35/1 the definitely it will be
damaged.,since the ratio test equipment takes few seconds
to indicate the ratio error the condition will be worst .
no doubt.
each ct have certain burden value indicated on it as 10va,
15 va etc.
consider the case of 35/1 ct. hhaving burden 10VA.
this means while 35A is passing through the primary 1A is
produced in the secondary. and and this current can create
a potential up to 10V.
then calculate the value of secondary current curresponts
to 1600A primary current.
the primary of 35/1 ct is not designed to meet 1600A. so it
shall be burn out.
if we keep the two cts as series connected and 35/1 cts
secondary shorted. then also primary winding of the 35/1 ct
will not withstand with the 1600A.( it will simply act as a
conductor because there is no secondary.
| Is This Answer Correct ? | 4 Yes | 1 No |
refer to IEC, CT can withstand for 1s if current at primary is 1000xIn, mean 35kA is maximal. saturated or not is depend on Rct and burden, need to be calculated
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s ramar
The ratio is nominal one. The CT is required to measure
fault current which is very high. So nothing will happen to
the CT when 1600 A flows in the primary.
| Is This Answer Correct ? | 0 Yes | 1 No |
some practicle study shows that the reactive power at the receiving end is not equal to the reactive power at the sending end.But according to theory the reactive power is exchanged by different parts of the network – capacitors and reactors permanently, but is never consumed or produced. Then Where that reacrtive power loss occuring?is there any formula to calculate reactive power loss?
what is the difference between NC & CNC machine.what is the difference between equipment & machine tool
what is the full form of KVAR
Relative synchronous generator
can you give me some names of projects which can be used in our daily life & which is having medium cost?
What is the use of conservater, bucchos relay, breather in a transformer?
8 Answers Bosch, Wipro, Zadco,
what irequirment need to be followed when working on live equipment
Why there is no provision of breaker in between primary of UAT and generator
Your B.tech marks is being given in CGPA grade. How is it calculated?
Can we connect more than one NGR at a time of different rating of generators. what is advantage or disadvantage.
WHAT IS THE MEANING OF BALANCED / UNBALANCED IN STABILIZER TYPES.
I know during Surge Impedance Loading maximum power is transferred through a transmission line and also Sending end voltage becomes equal to Receiving end voltage i.e Vs=Vr so my question is if both end voltages are equal then how current travels in such line hence how power is transmitted because flow of current needs Potential difference??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)