Two CTs 1600/1 and 35/1 are in series. while checking the
ratio test of a CT(1600/1),same 1600A will also pass
through the CT having ratio 35/1.
Will it be harmfull to the ct(35/1),if yes , what will
happen.CT secondary is shorted
Answers were Sorted based on User's Feedback
Answer / ullas
if 1600 ampere current is passed through the second ct
having turn ratio 35/1 the definitely it will be
damaged.,since the ratio test equipment takes few seconds
to indicate the ratio error the condition will be worst .
no doubt.
each ct have certain burden value indicated on it as 10va,
15 va etc.
consider the case of 35/1 ct. hhaving burden 10VA.
this means while 35A is passing through the primary 1A is
produced in the secondary. and and this current can create
a potential up to 10V.
then calculate the value of secondary current curresponts
to 1600A primary current.
the primary of 35/1 ct is not designed to meet 1600A. so it
shall be burn out.
if we keep the two cts as series connected and 35/1 cts
secondary shorted. then also primary winding of the 35/1 ct
will not withstand with the 1600A.( it will simply act as a
conductor because there is no secondary.
| Is This Answer Correct ? | 4 Yes | 1 No |
refer to IEC, CT can withstand for 1s if current at primary is 1000xIn, mean 35kA is maximal. saturated or not is depend on Rct and burden, need to be calculated
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s ramar
The ratio is nominal one. The CT is required to measure
fault current which is very high. So nothing will happen to
the CT when 1600 A flows in the primary.
| Is This Answer Correct ? | 0 Yes | 1 No |
WHERE IS THE LIGHTING ARRESTER SHOULD BE PLACED IN DISTRIBUTION LINES?
I want definition for ABT Meter (Availability Based tariff) ?
0 Answers Radha Regent Hotels,
How to get a multiplier in 11kv energy meter?
How to select earthing strip for 100kw induction motor ?
2- What are the percentages between excitation currents in phase (R, S and T) in ∆ and Ỵ connections in excitation Current test in transformers?
what are the protections used in power transformers of 5 mva and above
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
what are the reasons of low voltage during start the DG?
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?
What is on delay and off delay timers
can we start mulitple 3 phase induction motors with common starter?
where does core based current transformer is used? and what is the value of lux in a work station?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)