What happens if a three phase induction motor is suddenly
single-phased while running? Which type of winding
connection will be affected?
Answers were Sorted based on User's Feedback
Answer / sanjib pramanick
Motor is running as a single phase motor with lower speed
and creating noise. In this situation it will drawing higher
current. If it runs for long time then insulation may get
damage and ultimately burnout the winding.
| Is This Answer Correct ? | 98 Yes | 8 No |
Answer / rishav
when three 3 phase motor is suddenly single phased .
it will giving sound and its speed lower down. it
may also burn . and mcb or proction will come in
action. because current will rise very high in this
condition
| Is This Answer Correct ? | 69 Yes | 16 No |
Answer / rajesh shah
If a three phase induction motor is suddenly single-phased
while running, no distinct change will happen if it is
running under noload condition. You will just hear a
hunting sound and the the motor will continue to run with a
slightly lowered speed and increased current, but if the
motor is running under loaded condition it will stop down
and take excessive current due to single phasing and the
protection circuit will trip, if protection ckt is not
installed the motor will be ultimately burnt due to
excessive locked rotor current.
And note: This experiment is tested.
| Is This Answer Correct ? | 55 Yes | 2 No |
Answer / arvind
if 3 phase motor is suddenly single phased while running
then two phase will supply current to the motor, but it
will draw more current from the main supply,and the winding
will burn out
| Is This Answer Correct ? | 38 Yes | 2 No |
Answer / syed
Three phase motor suddenly runing single or two phase.Motor
will get over heat and giving noise.this case if we have
protection like breacker it will trip other wise motor will
burn out
| Is This Answer Correct ? | 19 Yes | 3 No |
Answer / derek
For a Delta connected motor two of the phases (coil sets)
will see normal curent and the other phase will see 200%
current. The supply current in the two remaining phases
will be 173% of normal current. In this situation one coil
is across AC power and the other two coils in series with
each other are in parallel connection with the first.
For a Star connected motor tow coils will carry %173 of
normal current while the other leg has no power. The two
active supply lines will have %173 of normal current.
If the motor is running at %70 load the current may not be
high enough to trip the overload protection and the motor
will overheat.
Slow blow overload protection should be sized to trip in
these conditions.
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / rahul
If protection is proper then it will operate and stops the
motor. If there is no protection which is the normal case
in LT motors, then winding will burn there are two diffrent
pattern which will apear depending on the type of winding
connection i.e. delta or star.
You will find most of the winding failure in LT motors
happens due to single phasing.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / stefan
#4
Usually when talking about "single-phased" motor, it means
that two of three phases are connected. In these cases, the
motor will slow down, and the phase currents for the
remaining phases will be increased. I don't know how much. I
am also not sure if the overload device would cut-off the
motor from power supply. Unless problem is not noticed, the
motor will most likely burn. When the motor is opened, you
should be able to see that 2 of the 3 phase windings are
black, and one is good looking (if motor is Y-connected)
| Is This Answer Correct ? | 16 Yes | 13 No |
Answer / madhusudhana
A three phase motor will continue running if a phase is
lost. Most three phase overload relays are not intended to
provide true single phase protection, so the most likely
scenario is the motor will run at reduced speed for some
time and will eventually overheat and fail. A three phase
motor will not start, on its own, with only single phase.
However, if the motor shaft is "manually" spun it may begin
to turn and accelerate slightly. If the motor shaft is
turned backwards then the motor would start in reverse.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / rajesh sharma
1.if motor conected in STAR than motor two winding burn
2. if motor in DELTA motor one winding burn
3. time duration is depend on load for burning
4. in star R phase is blown than y/b winding burn because
that winding get 440volt and take to much current
5. delta if r phase blown than y pahse winding burn because
only that winding get 440 supply other no.
| Is This Answer Correct ? | 3 Yes | 0 No |
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
Will any motor burn if voltage provided is lesser than the rated voltage???? If yes, then how is speed control possible with voltage control
how much up to LT Voltage range?
Baud rate is used to descrice...?
What is circuit breaker failure protection?
What is meant by sotf,lbb,power swing,pole discrepency,auto reclose?
1 Answers Bunge, Electrical, Omega, TCS, TNEB Tamil Nadu Electricity Board,
What are the types of earthing? Explain dagramatically.
sir plz send some previous year questions of jspl.
Sir, My doubt on cable sizing calculation, Load:74 KW calculated cable 1 run 50mm2. Now client asking us to reduce cable size by increasing runs. Sir, My question now when my mind strikes with 2 options 1) Divide load 74/2 = 36 and calculate cable for 36+36 making it 2 runs or 2) Simply i can divide 50mm2 /2 ie. 2 runs of 25mm2 Please suggest me sir
A 10 MVA, 66KV, 50Hz, Y-connected 3-phase alternator has synchronous reactance of 0.635 Ù. It is working at full load at 0.8 lagging p.f. condition. Find torque angle, neglect armature resistance.
How do you connect the capacitors on polyphase circuits?
What is a neutral
4 Answers Adani Ports, Dr Reddys,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)