what happen if generator exitation lost?
Answers were Sorted based on User's Feedback
Answer / shiv
when there is no excitation ther will be no magnetic field
setup as a result of which no EMF will be induced which
means there is no output available from the generator.
| Is This Answer Correct ? | 17 Yes | 4 No |
Answer / sunil kumar sinha
If the excitation of generator is lost, it will continue to
generate power by taking excitation from grid. The flux
will pass through the surface of rotor which will cause
excessive heating of rotor. Further, around moon slots the
current will jump and may cause over heating around moon
slots of generator rotor beyond limits.
There is possibility of insulation failure of rotor winding
if operated for longer period at higher load, hence loss of
excitation relay is a must protection for generator. This
relay is further monitered by excitation supervision relay
in many of sets.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / jagatheesan k
if excitation lost generator will draw power from grid(ie.,it draws reactive power from grid)and run as induction generator(runs at a speed more than synchronous speed) .
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gunnam santosh
if excitation is removed also it will induce a small emf as
we basically use eletromagnets it contains some residual flux.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajasekhar
am takin a synchronous generator
in general a syn. gen operates on prinicipal of synchronism
which obtains when we excite it with any other source ...if
directly excitation is lost there wil not be any alternating
flux which plays a main role with out no operation takes place
| Is This Answer Correct ? | 3 Yes | 3 No |
If the excitation of generator is lost, than emf will not
be induced in alternator. Than we need to do excited
alternator by Outer DC voltage.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / umesh
in the generator the exitation is the main source to
genrate the EMF, whenever the exitatio got lost then there
is no magnetic field, NO EMF will be built,
| Is This Answer Correct ? | 1 Yes | 4 No |
If an induction motor is restarted before its rotor stop rotating, then what will be the amount of current drawn? Is this current will be the same as motor starting current?
HOW THE AC GENARATOR CAN GENARATE REACTIVE POWER,HOW CAN WE CONTROL IT.AND OTHER SOURSES OF REACTIVE POWER GENARATIONS ARE WHAT.
HOW TO CONNECT THREE PHASE OVER LOAD RELAY FOR SINGLE PHASE
The maximum demand of consumer is 2 kW and his daily energy consumption is 20 units. Its Load Factor is (1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
Why Motors are generally supplied with 3 core cables??? why not 4C??
Where burned of electricity,when,who, & why.
can we run a motor rated 50Hz,415vac,1440RPM At higher speed then rated on name plate with the help of VFD /drive on long term basis.wheater it will effect the motor life
1KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
16 Answers Ecil, Engineers India, MahaDiscom,
how many types of accuracy class in ct? what is meaning of 5p20?
how to measure the dc current?
what is the method of earthing of a transformer using electrodes?
how to prepare PPM schudule
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)