WHY FLEXI LINKS ARE USED INBETWEEN GENERATOR TERMINAL
OUTPUT & BUS DUCT CONDUCTOR.
Answers were Sorted based on User's Feedback
Answer / surender singh
In output of Generator terminal and Bus duct ,we use flexi
links ie no hard connection because to avoid the transfer of
vibration of generator to bus duct.
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / shali
That have also something to do with avoiding high tenssion
on the generator terminals due to the physical weight of
the hard busbar. Plus, limiting the transfare of the
generator vibe to the bus.
Is This Answer Correct ? | 1 Yes | 0 No |
IN A DY11 GROUP DISTRIBUTION TRANSFORMER WITH NEUTRAL EARTHED, WHAT WILL HAPPEN TO THE SYSTEM VOLTAGE & THE EQUIPMENTS IF EARTH GETS OPEN ON LOAD?
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply
any one have papers of hpcl or sailof ELECTRICAL ENGG.
The error in a single phase energy meter where pressure coil lags behind applied voltage by 88 degrees and pf is 1) upf 2).5lag
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
60 watt bulb and 1500watt iron which device has more resistance & why
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
an amazing situation was faced when an alive distribution panel with 415 volts and carrying almost 200Amps has become short and this metal cubical showing 220 volts against neutral and earth. to redress any confusion i checked the panel with help of single 200watts test lamp which also glowing with max.intensity b/w neutral & metal body of DB. amazing situation is that i hold the DB firmly more than once with necked foot means without insulated shoes but not received any electrical shock. whereas our all running gen sets neutral points also proper grounded and this short DB was completely earthed , this is beyond my understanding . any body explain how is it possible . our running gen set neutral also grounded firmly
how to checking earth restence with earthtester
Dsitrubution transformer minimum IR value
Differance between ELCB and RCCB?
block diagram of 2 ups system connected in hot stand by mode?