Why we use a shunt capacitor or synchronizing Motor To
Improve a Power factor pls reply me in this mail
dinesh_elect_eng@yahoo.com
Answers were Sorted based on User's Feedback
Answer / sandeep
shunt capacitor & synchronizing Motor can be operated at
leading pf (it takes leading current) .
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / k.prakashchandra
The above answer given by is irrelevant ,as the word
'synchronizing motor' caught me on the wrong foot.Almost all
loads are inductive and hence the pf of the system is always
lagging.To negate lagging reactive load we have to include
capacitive reactive load using either shunt capacitors or
over excited synchronous motor.
Is This Answer Correct ? | 2 Yes | 0 No |
Sinchronous motor is used to improve power factors.
Most of our equipments & electrical machinary are inductive
load i.e. in industries,institutions,large offices &
commercial buidlings are having large electrical system .
To improve the cosine angele between voltage & current we
are puting capacitor bank & Sychronous motor.
Sub-stations are having above power factor improvement
devices.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
The synchroscope consists of two phase stator. The windings
are at right angles to one another and they are connected to
incoming generator.To have a rotating field ,the current in
one winding is made to lead the current in another by 90'
using a capacitor, as in a single phase motor.The polarising
winding in rotor (pointer) is connected to running generator.
Is This Answer Correct ? | 0 Yes | 0 No |
What happened when the field winding of dc series motor is open?
What are the different modes of plc processor?
low frequency protection why recomend?
the relationship between phase and line voltages in a 3 phase generator is expressed in what formula?
what is the difference between delta delta and star delta connection transformer? why we use delta delta transformer since it need earthing transformer for grounding?
What happened when a three phase induction motor work on two phase supply.9
what happens if we give 1-ph supply for 3-ph Bridge rectifier...??
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
i HP = ?? 746 watts or 735.5 and how??
1. alternator has full load regulation of 4% when pf of the load is 0.8 lag, 1500 rpm. full load regulation of 1400 rpm for 0.8lag will be ________ ?? 2. torque angle of a sync m/c operating from a constt voltage bus is usually defined as space angle between _______ . 3. method most effective in finding out no load losses in large DC shunt motoris ______ . 4. current carrying capacity of fuse material depends on ______ . 5. coil has res. 10 ohm, inductance 1H. what wil be current after 0.1sec after switching on to a 500V DC SUPPL ? ? 6. effect of phase lag compensation on servo systems ___________ . 7. rotor of a dc machine is usually supported upon ______ . 8. DC motor is preferred to AC motor in which application ?? 9. 3 nos of 10:1 Xmer are connected in Star-Delta to supply a load at 230V.the supply voltage must be ______ . 10. voltage source produces max current in which circuit. 11. cal. power, if current and voltage are out of phase by 90 degree. 12. suitable length of Xmission line of power at 66 KV. 13. Which of the theorm helps in simple computation when the load across a ckt is varying ?? 14. what is the adopted line length for power Xmission of power by cables ??
How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
Distinguish between neutral earthing and equipment earthing?