Answer / sandeep
shunt capacitor & synchronizing Motor can be operated at
leading pf (it takes leading current) .
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / k.prakashchandra
The above answer given by is irrelevant ,as the word
'synchronizing motor' caught me on the wrong foot.Almost all
loads are inductive and hence the pf of the system is always
lagging.To negate lagging reactive load we have to include
capacitive reactive load using either shunt capacitors or
over excited synchronous motor.
| Is This Answer Correct ? | 2 Yes | 0 No |
Sinchronous motor is used to improve power factors.
Most of our equipments & electrical machinary are inductive
load i.e. in industries,institutions,large offices &
commercial buidlings are having large electrical system .
To improve the cosine angele between voltage & current we
are puting capacitor bank & Sychronous motor.
Sub-stations are having above power factor improvement
devices.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
The synchroscope consists of two phase stator. The windings
are at right angles to one another and they are connected to
incoming generator.To have a rotating field ,the current in
one winding is made to lead the current in another by 90'
using a capacitor, as in a single phase motor.The polarising
winding in rotor (pointer) is connected to running generator.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is RCBO?
if two transformers are parallel & both have fault short ckt. impedance of 50KA in each case will it increase or decrease show example?
what is the voltage and ampere rating of all range of HT conductor?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
We have 3 Gensets 1.500kva,2.380kva,3.250kva How can we connect in common busbar&we have variable load.
What is the 415V AC Soft starter? Explain with an example?
why we use two slope(differential & restraining) in differential relay.but in busbar protection differential we are using only one slope?please explain
does magnetic interlocking take place in an induction motor ?
How can two 3 phase transformers of same KVA and Voltage be connected in parallel?
0 Answers Bernhard Schulte Shipmanagement,
When dc supply is fed to rotor of the alternator how it work?
hi friends how 3 phase converter functioning ?what is working principle of rotory phase converter ?
please tell me how a surge protector work on a DC 48Volt.? please describe briefly.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)