what we happen if 400 kvar cpacitor banks are on in manual
mode and there is no load on mains ??????????????
Answers were Sorted based on User's Feedback
Answer / vinod sharma
If the bamk is on mannual it will lead the voltage.
Due to this the power factor will cross the limit 1 and
with this losses will increase.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / rahul shukla
VOLTAGE WILLL RISE AND ALL LOADS i.e motors ect. get
overfluxed as v/f ratio will be high
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ashok
power factor is leading and average power factor decreased
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / er. ankush miglani 9718151073
if all this happen the power factor increases from unity
and the supply is fed back to the system i.e. the load
becomes the source.
or
when capacitors charge to its peak value they will not get
any path to discharge and remains charged i.e. nothing will
happen.
or
practicaly try karne ka yaar.........
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / chandra
The load power factor becomes leading and load becomes
source and power is supplying to the system instead of
receiving.
Is This Answer Correct ? | 1 Yes | 3 No |
how braking & making capacity of circuit breaker are calculated?
Why should we use Star-Delta connection in step down power transformers?
how much Amp we can put in 1200kva generator?
how to decide cable rating? send me cable size,ampere rating data
Since phi is the angular displacement between V & I, then why we use phi in power triangle ie. when showing active, reactive & apperent power in triangular manner & if it is ok then where is V & I in the triangle.
what is power factor
what is phase voltage and phase current what is line current and line phase
what happen if any one phase of a slipring induction rotor winding is open?is it start or won't?
requirements for making parallel operation of Uninterrupted power supply
What is the meaning of coupling and decoupling in the context of power flow?
How efficiency of thermal plant can be improved?
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?