What are the voltage values for LT,HT,EHT and other
voltages??
Answers were Sorted based on User's Feedback
Answer / anbuselvan
Low Tension=upto 1KV
High Tension=upto 11KV
Super Tension=22KV-33kv
Extra High Tension=33-66kv
Extra Super Tension=beyond 132kv
Is This Answer Correct ? | 165 Yes | 39 No |
Answer / ishan patel
LT voltage is upto 415 volts.
HT voltage is upto 220KV.
EHT voltage is upto 1100KV.
Is This Answer Correct ? | 179 Yes | 102 No |
Answer / priyadoss
LT - 230v,440v,upto600v
HT - 1.1kv,3.3kv,6.6kv,11kv,33kv,66kv
EHT - 110kv,233kv,440kv
Is This Answer Correct ? | 86 Yes | 36 No |
Answer / shashi nath jha
LOW TENSION (LT)= 1000 (1KV)
HIGH TENSION (HT)=11000 (11KV)
SUPER TENSION (ST)=22000-33000 (22KV-33KV)
EXTRA HIGH TENSION=33000-66000 (33KV-66KV)
EXTRA SUPER TENSION=BEYOND 132000 (<132KV)
Is This Answer Correct ? | 45 Yes | 8 No |
Answer / natarajanramkumar
1.L.T (Low tension)=upto 1000 volts
2.H.T (High tension)=upto 11,000 volts
3.S.T (Super tension)=from 22,000 volts to 33,000 volts
4.E.H.T (Extra high tension)=33,000 volts to 66,000 volts
Is This Answer Correct ? | 55 Yes | 27 No |
LT upto 440V
HT upto 66 kv
EHT above 66 KV upto 1200 KV (under testing)
Is This Answer Correct ? | 41 Yes | 29 No |
LT-LOW TENSION---- NOT EXCEEDING 250V
HT-HIGH TENSION---MORE THAN 650 V & UP-TO 33 KV
EHT-EXTRA HIGH TENSION-MORE THAN 33KV
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / raja
In India IS specifications are followed which has BS
standard as base.
Normally AC 50 V - 1000V volts are considered LT .
1kV to 66 kV is considered HT and
Above 66 kV is EHT
Voltages below 50 volts is considered Extra low tension
Is This Answer Correct ? | 18 Yes | 8 No |
Answer / sr
Low voltage upto 1.1kV
Medium Voltage from 6.6kV to 33kV
High Voltage from 66kV upto 132/110 kV (in Karnataka)
Extra High Voltage from 220 kV & above.
Is This Answer Correct ? | 24 Yes | 15 No |
Answer / k.gurusamy
LT 230V,433V
H.T 6.6KV,11KV
S.T 33KV
EHT >66KV
Is This Answer Correct ? | 11 Yes | 3 No |
my 10 hp submersible pump is tripping when connected through ELCB.I have checked the megger value of the coil's with body.It was found to be 0.2mega ohm.that is leakage is there.But when connected to mccb it is not tripping.no leakage current in the motor.Is it safe to connect to mccb? what are the problem's will arise if future?also tell me in ELCB no neutral is connected to motor.than how ELCB was working?
which one is the most common system for secondary ditibution
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
what will happen if ac power supply is given to the rotor of an alternator
synchronous motor of 13.5MW having which type protection? and how to set relay?give me relay setting calculation for different protection for this motor assume efficiency,power factor and other term if neccecery
what is ten delta test? what is the significanse of it
what is the use of static frequency converter and static excitation equipment? and where it is employed? for what?
Is RTCC panel needs any control supply.
what is iron loss?
how is working the APFC when varying the load?
what are the advantages by using IGBT in VSC HVDC than thyristor in conventional HVDC
what is relay