how to check the earth resistance value& what is the
minimum earth resistance for good earthing sysytem.
Answers were Sorted based on User's Feedback
Answer / jaydeep parmar
value of the earth pit should be less then 2 ohm and earth grid value should be <1 ohm
| Is This Answer Correct ? | 428 Yes | 59 No |
Answer / tauseef tarique, engineer(e)
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 8 ohms.
| Is This Answer Correct ? | 318 Yes | 43 No |
Answer / pandiyarajan
Grid resistance value should be lessthan 1 ohm
| Is This Answer Correct ? | 209 Yes | 31 No |
Answer / aruna devi
By using earth megger .It should be less than 2ohm.
| Is This Answer Correct ? | 227 Yes | 72 No |
Answer / bhavini
earth tester use for measuring resistance of earth pit
should be less than 1 ohm.
| Is This Answer Correct ? | 105 Yes | 26 No |
As such there is no any standard of earth resistance value,
Its varies on different type of soil resistivity. Idley it
should be 0, but in different kinds of soil for electrical
equipment it should be better to below 10 Ohms and for
electronic equipment it should be better to below 5 ohms.
| Is This Answer Correct ? | 100 Yes | 28 No |
Answer / ramaraj.g
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm but the
permissible value is less than 5 ohm. For rocky areas it
should be less than 5 ohms.
we using the DMM in check the L - N , N- E ,E- L
this small calc
L-N - 230 v
N-E - BELLOW THE 2 VOLTS IS GOOD ERATH CONN
E-L - 230v IS RECONFORM TO GOOD EARTH OR NOT
L-N = E-L
| Is This Answer Correct ? | 77 Yes | 11 No |
Answer / bk sharma
It should be near <0.5 ohm for good earthing.
| Is This Answer Correct ? | 64 Yes | 11 No |
Answer / bhanu
earth testers are used. and it is checked wheathe earh
resistance range is from 1-2 ohm or not.
| Is This Answer Correct ? | 83 Yes | 39 No |
what happen to the voltage and current in all phases when an earth fault occur in a phase in three phase three wire system(delta connected)...
what is the id1 & id2 setting in differential protection relay of CSPC?
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
What are the types of relay ?
What are interpoles and commutation windings?Why r they used?
What is the difference between "Earthing" and "Neutral"?
What Should be the value of Vector Surge angle at Tripping and how to calculate it?
what is the relation between voltage & frequency
how to calculate micom relay earth falt time and current sertting
what is the different between Switch & Circuit Breaker?
How to calculate the fuel consumption for 600kva DG genset which connecting with 25%load?
what is the working principle of DC generator ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)