Answer / divay chadha
3core-185 sq. mm
Calculation:-
Current at HT = (1500 x 1.4)/ (33*1.732)
| Is This Answer Correct ? | 267 Yes | 142 No |
Answer / s.srinivasan
Generally HT cable sizing is not done based on the full
load current of the equipment but based on the prospective
fault level. For a 11kV network, generally it shall not be
less than 150sqmm XLPE.
Fault level at 11kV(furnished by respective EB)=100 MVA(say)
Details on EB's fault level can be obtained from EB.
Therefore fault current= 100*1000/(SQRT(3)*11000)
= 5.25 kA
Short circuit current rating (for 3-sec duration)of HT 11kV
XLPE cables with Alu conductor is as below:
95 sqmm: 5.16 kA
120 sqmm: 6.51 kA
150 sqmm: 8.14 kA
| Is This Answer Correct ? | 139 Yes | 29 No |
Answer / j.kesavan
please slect your cable in 11kv py side how much current
check first after you slect your ht cable.
| Is This Answer Correct ? | 93 Yes | 42 No |
Answer / neeraj tyagi
simple for 11kv
Amp in HT= kva*1000/ 1.732*11000
= size for 78 amp HT XLPE 3 core 95 mm2 higher side.
| Is This Answer Correct ? | 92 Yes | 51 No |
Answer / gb
11kv----13 amps on primary side
1500 kva 1.4 = 2100 amps on secondary
| Is This Answer Correct ? | 43 Yes | 29 No |
Answer / madhu mohan
First calculate the current of primary side(HT) and derate the cable by atleast 0.7.
Eg:1500*1000/(1.732*11000)=78.73A
Current I after Derating =78.73/.7 =112A (0.7 if laid on the trays or value will vary if buried in the ground).
Cable equivalent to rating has to be selected.
Now Short circuit withstand capacity (sq. of I X t in sec) has to be checked from the cable catalogue.This value of cable should be higher then SC withstand capacity of the ground usually it is 50KA.it less go for next size and finalise.
| Is This Answer Correct ? | 32 Yes | 24 No |
Answer / sairaj
90 Sq.mm Al Ar XLPE cable is sufficient. But as per statutory norms for 11kV, 185 Sq.mm Cable is considered.
| Is This Answer Correct ? | 15 Yes | 9 No |
Answer / murugan
How to select different types of Transformer KVA rating,
with matching cable size in Primary and secondary..?
100kva TR = cable size with full load amps rating
150 kva TR = ???
250 kva TR = ???
500 kva TR = ???
750 kva TR = ???
1000 kva TR = ???
The cable size
95 sqrmm
120 sqmm
150sqrmm
185 sqrmm
240 sqrmm
300 sqrmm
400 sqrmm
500 sqrmm
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / engr. md n h shabuj
S=(Ish *√t)/K
=(10.49*√1)/0.143
=73.35
=75Rm cable
Ish =P/ (√3*V* % of Z)
= (1500*10^3 )/( √3*11*10^3*7.5%)
=1049A
Ish =1049*10=10490A=10.49KA
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / saad yar khan
Where can I get the chart for selecting HT cable based on 1500KVA i.e 78Amp
| Is This Answer Correct ? | 1 Yes | 1 No |
from which formula we select a capacitor rating?
what is residuel magnetism
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
I just purchased a 4 position cam switch to be used to operate a 3-speed blower motor. The motor is a 10 amp motor and has 3 wires that are used to control speed. The cam switch was rated at 660V 20 amps but when I received it, I noticed that it has AC-15 operational current rating (Ie) of 4/5 amps. If I am reading the label correctly. the 4/5 amps is related to 440v/220V (Ue). Other ratings are AC-3: 5.5A, AC2: 7.5A and AC-4: 1.5A. My questions are 1) Is it safe to use this switch with the motor I have 2) what is the difference between the 20 amp Ith ratting and the Ie operational ratings?
what is relation between vector group of transformer and its load hormonics?
what is the main difference between power devices and signal devices
how bucchos relay works in a transformer
I need a formula to calculate the size of cable as per load but in the terms of length. Please Reply me as i search lot of sites but i did not get the answer.
Why does the Solid state Rectifiers for 3-ph brake motors sometimes have 2 & sometimes 3 output terminals?
what is the contact resistance of sf6 circuit breaker??
What is ST and specify its range of voltage.
WHAT IS IEC? & WHAT IS BENEFIT TO PRODUCT FROM IEC?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)