how to check the earth resistance value& what is the
minimum earth resistance for good earthing sysytem.
Answers were Sorted based on User's Feedback
Answer / sarav
We used Earth Megger for measuring the earth value.The
value of the earthing is vary depends upon the place.
In residential towers we should maintain the earth value is
below 2 ohm.
Is This Answer Correct ? | 19 Yes | 3 No |
Answer / k. naresh reddy
We used Earth Megger for measuring the earth value.The
value of the earthing is vary depends upon the place. we
should maintain the earth value is
below 1ohm.(0.1 ohm is good earth resistance value)
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / rahul patil
EARTH RESISTANCE FOR GOOD EARTHING IS LESS THAN 5 OHM & GRID
RESISTANCE IS LESS THAN 1 OHM
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / kobina k. mensah
The earth resistance is checked using a earth resistance
tester and how good an earth depends on the type and number
spicks, voltage, soil and other facts.
Is This Answer Correct ? | 14 Yes | 6 No |
Answer / dipeandra deepak
normly earth res.value for an industrial area is 1 to 5
res.for rock sail area and residential area, this value is
8 and 1-3 res respectively.further ithink this depends upon
ur mant. capability. this can be maintened by checking
earthing pit time to time. it also depends the size of
earthing patti and the load capicity set against it.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / kallesh
By using Earth Megger to check the earth resistance and
Minimum earth resistances for good earthing is 0 ohm to 5 ohm.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anil
Now a days all telecommunication installations insist for value <0.5 ohms.
However domestic installation is ok upto 2 ohms.
The easiest way to measure the value of domestic earth is using a multimeter measure voltage across n-e it must be less than 5 ohms.
Is This Answer Correct ? | 2 Yes | 0 No |
What are the rating wise protections required for Generators from 600KVA to 2000KVA
How many points can we have in AC Circuit? Show by giving suitable example?
How do you find HT and LT sides of a distribution transformer only by looking at it from outside?
for preparation of design note of 11 / 220 kV , 3 phase, 63 MVA transformer how can calculate or consider the iron losses and copper losses
how we can calcultae the short circuit level for bus bar
0 Answers Jaiprakash, Panorama Apparels,
how much earth resistance consider to commissioning the transformer?
what will be the minimum megger value for 132 Kv (earthed) potential transformer
Brief use of isolation transformer & how it works.
what are different types of alternator and discuss about the methods of cooling
16 Answers Bhel, Jindal, L&T, Nalco, Vedanta,
1.generator rated as 1000 mva,11kv .8 pf what will 0.8 pf will indicate? 1.max pf it can supply 2.min pf it can supply like this 4 options there what is answer.explain
what is the use of commutator in dc motor if we supply ac ? commutator is used to convert ac to dc.and it is used to arrange the flux in unidirectional in case of dc supply. if we give ac as supply to dc motor what is the use of commutator?
For 415v,3phase,22kw rating of motor how to calculate MCCB rating