Answer / revansiddappa p.h.
Basically contactor is used to make and break the circuit
like any switch. For handling higher current and volatge we
use contactor; not only for motors.
Between VFD and motor; contactor is not required.
Because VFD will have features like enable and disable.
VFD will use IGBT's inside for switching application.
As IGBT's are semiconductor ; switching is fast compared
to electromachanical type contactor.And IGBT's handles
larger currnts.By enabling or desabling of VFD we can
Start/stop motor(with speed command). If contactor is used
there will be some time difference in swithcing ON/OFF of
IGBT and contactor which may lead to failure of IGBT and
motor winding and insulation. So it is meaning less to use
conatctor and also cost will be more.
Is This Answer Correct ? | 23 Yes | 4 No |
Answer / nandan d shanbhag
Due to electromechanical bouncing of the contactor
contacts , voltage spikes are generated which in turn will
result in failure of smiconductors in the drive. However
due to eletrical regulaton if contactor needs to be
provided for electrical isolation then there must be delay
of 1 sec before starting the inverter after contactor is on
and contactor should be made of atleast .5 second after the
inverter is made off.
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / shailesh
vfd is a variable frequency drive,which not provided
contactor because there use a thyristor.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / jayaseelan
This will cause unnecessary wear on the contactor and
there will always be a slight delay while the inverter
initialises.ie.if contactor placed in between vfd and motor
response time of contactor gettting on is slow compare to
vfd response speed so return current wii affect the
electronic bords.thats y contactors not not used in output
of vfd.
Is This Answer Correct ? | 6 Yes | 6 No |
Answer / jayaseelan
This will cause unnecessary wear on the contactor and
there will always be a slight delay while the inverter
initialises.
Is This Answer Correct ? | 4 Yes | 22 No |
what type of motor used to move a 1 ton gate? and relate ratings with load.
What do you mean by ratio correction factor of instrument transformer?
what are the reasons of low voltage during start the DG?
How it can worked plc based electrical system And which type of software using.
How is the resonant peak, resonant frequency, and bandwidth determined from nichols chart?
how we could know that generator running anti clockwise with seeing the rotating direction of prime mover or engine
How to apply 'c' license and also explain what is difference between 'c' and 'b'license.i am also working in one of the private company.i have finished my diploma in 2014 .i have already finished in ITI electrician course.....
Why a transformer is known as a static device?
how ups works ? various parts of ups and working principle
Zone of protection and tripping scheme of arc protection relay.
why the all high voltage transformers are in 11kv , 33kv , 66kv, 132kv like that
What is the operating range of voltage and current in grid supply in India?