how to check the earth resistance value& what is the
minimum earth resistance for good earthing sysytem.
Answers were Sorted based on User's Feedback
Answer / kalpesh
the earth resistance can be checked by using earth tester
04 spike method.
as far as minimum earth resistance value is concern, it
depends on teh type of gazet connected to this earth pit.
however the resistance should be as low s possible
Is This Answer Correct ? | 5 Yes | 5 No |
earth resistance of individual earth pit should be less
than 5ohms and when it is connected with grid should be
less than 1 ohms
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / guru
There is not one standard ground resistance
threshold that is recognized by all agencies.
However, the NFPA and IEEE have recommended
a ground resistance value of 5.0 ohms
or less
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / robeesh
Earth Resistance test to be conducted on summer conditions to achieve the correct value by using an earth resistance tester (From Megger/ Sanwa/ Fluke). The value should be less than 1 Ohm for electrical earth pits and less than 10 Ohm for Lightning protection System. Procedure for testing should be as per the equipment.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nasir sharif
The earth resistance value can be checked by the use of
earth resistance tester (called megger earth tester). The
best earth resistance should be less than one ohm & ideally resistance is Zero ohm but the
permissible value is less than 5 ohm
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / chanchal tiwari
the earth resistance should be less than 1 ohm. if we using
digital earth resistor, then one common method used as
three terminal type and the distance between these three
terminal should be 20 to 30 meters.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / prince
Switch on the multimeter, and using the dial on the front, select the resistance function. The multimeter will have two probes with metallic pointed ends. Place the probes on either side of the earth wire. The display on the multimeter should show a low resistance of approximately 0.5 Ohms. If the resistance is significantly higher than this, the wire is faulty and needs to be replaced.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / malik
by using mager we can find the value of earth resistance.
there are three types of resistance
1}low resistance
2)medium resistance
3)high resistance
earth resistance comes in LOW RESISTANCE it should be blow
then 1ohm.
Is This Answer Correct ? | 2 Yes | 6 No |
i am completed in B.E(Electrical and Electronics Engineering) with 8 months experience in Quality Control Engineer at Bharathi Industries,Coimbatore.
How to determine earth fault level to set relay for a normal distribution system of 11 kV , 100 A load????????
WHAT IS A COLOUR CODING OF 3 CORE CABLE
WORKING PRINCIPAL OF MCB
what is mean by transition resistance of transformer?
HOW TO SIZE THE TRANSFORMER OR WHAT ARE THE STEPS INVOLVED IN FINDING THE SIZE OF THE TRANSFORMER FOR GIVEN LOAD SAY 2000KW ?
Which Programming software are use for Allen bradley PLC's?
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
what is soft starter? what is the difference between soft starter and star delta starter?
How can we calculate cable size in Low voltage & high voltage
0 Answers United Breweries UB,
why white color LED light is not possible?
how many power plants in andhra pradesh,how many types and there capacity