How to calculate the motor winding resistance ?
Answers were Sorted based on User's Feedback
Answer / dharmendra raninga
Please give the answer of this que.
Is This Answer Correct ? | 99 Yes | 55 No |
Answer / m.ramesh
how to calculate the motor winding resistance
Is This Answer Correct ? | 16 Yes | 6 No |
Answer / manik shinde
first apply the reted voltage & current then once we know
the v & I by voltmeter & ammeter, calculate resistance by
R=V/I.
Is This Answer Correct ? | 91 Yes | 83 No |
Answer / mike
you can find the resistane by using ohms law but that only
applies to a resistive load. ie.,electric heaters. for an
inductive load you'll have to call manufacture or use an
ohm meter. on a three phase motor the resistance on all
three legs should read the same or very close and on a
single phase the run and common should equal up to what
your start winding ohms are
Is This Answer Correct ? | 13 Yes | 5 No |
Answer / myo
The static resistance for the stator you can simply connect
the multimeter between 2 phases and arrive at the phase
resistance. Usually motors windings are delta connected. You
multimeter reading is 2/3x phase resistance.As for the rotor a
squirrel gauge motor has no rotor windings and slip ring
motors have windings connected to slip rings. In the second
case apply the same principle if you know whether the
windings are star or delta connected. For complete
determination of the equivalent equivalent circuit conduct the
no-load and blocked rotor tests.
Is This Answer Correct ? | 33 Yes | 27 No |
Answer / gunasekaran
first we have calculate the efficiency.
then we calculate the core loss.
loss is Isqr*R
we know load current and loss then we can calculate the wdg
resistance of the motor this is app.method not correct.
for transformer also same like that.
we can get the loss and efficiency of the motor from
manufacturer.
Is This Answer Correct ? | 22 Yes | 16 No |
Answer / ashour ghareeb
dc motor has four wire tow for field and other for armature
CONNECT OHMMETER,SLOWLY MOVE THE ROTOR,
IF READING IS FIXED,IT WILL BE FOR FIELD
IF NOT FIX,IT WILL BE FOR ARMATURE
SERIES-WOUND motor resistance is:
ARM.RESISTANCE
~100 Ω
FIELD RES.
~1 Ω
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / ramesh ravichandran
in case you want to calculate induction motor winding resistance..
to get accurate value of DC resistance, firstly do block rotor test so winding of the motor get heated up at rated current..
immediately remove AC supply lines and connect DC lines across any two phase and apply 50 percent of the rated current of the IM to get the accurate DC resistance
convert the DC resistance into AC resistance by a factor of 1.2..
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / muhammad kamran
although ohm-meter test is thorough enough but its not
complete...to find true result 1st ohm-meter reading is
taken and then in 2nd step a low voltage ac signal is
applied (using step-down transformer)normally 6:1 of
original operating voltage both voltage and current is
taken and Z-l(total impedence is taken) as unit is
performing in ac region not dc while ohm meter is dc
test.... why use this test?
not always the clear result is given by ohm meter test. a
winding may show balance state by ohm-meter but any
irregularity can be detected by AC-impedence test to be sure
Is This Answer Correct ? | 14 Yes | 15 No |
What will happen when a DC series motor suppllied by an AC source ?
WHY IN THREE PHASE CABLE 440V CURRENT FLOWS IF IN ONE PHASE 230V CURRENT FLOWS ???
why neutral grounding transformer is used for generator and why it is not used for transformers?
What is the cut-off rate?
we all know that in capacitor there will be no ay physical connection between the two electrodes of the capacitor ,and the charge is stored between these electrodes during charging , so with out any physical connection how these charge is transferred from one plate to the another plate during the discharge?????
If my sfu is 64 Amp & its link is 32 Amp then at what amp.my sfu will trip???
What is the effect of leading power factor for power transformer & D.G?
As the one point of eac phase winding is connected to each other in satr connction. Even if that at distribution side collesion of two diff phases result in to blast. Why?
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
i have 60Hz motor, can i run it at 50Hz power supply ???
Lt trivector meter with ring type CT.Spec of meter are 3x240 v, -/5A. Ring ct spec. are 60/5A, line voltage- IL .66/3.0KV..what is the multiplying factor
how can we calculate the reactence of the current transformers?