One amps in HT is equal to how manys amps in LT
Answers were Sorted based on User's Feedback
Answer / shahid
It depends on Voltage rating.
As 11 KV
Example.
we used Transformer 11/0.433 KV ,500 KVA, Its Primary side
26.2 A and its secondary side 666.2 A.
Its mean 1A in HT equivalent to 25.4 A
| Is This Answer Correct ? | 147 Yes | 22 No |
Answer / j.prabhakaran
if we knows the primary & secondary turns or voltage ratio
of transformer by using the formula
n1/n2=i2/i1=v1\v2
we could find the answer..
| Is This Answer Correct ? | 12 Yes | 5 No |
why are the a.c.series motors preferred for electric traction
what is divercity factor?
what is the method of earthing of a transformer using electrodes?
Between Star-Delta & Star-Star Power transformer which one is efficent for Earth Fault?
how to calculate the no. of turns in secondary side of CT?
what is the use of vcb & isolator in substation?
how the harmonic pluses take place in the flow of current
what is mean by dry frequency
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm
What is called limb of a transformer?
How do apply electrical 'c'license......pls advice
Write masons gain formula.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)